fry80657

Can someone please explain the diversity maximum demand topic, it really confuses me! For instance in most properties I wire I have 9kw boiler 45A, 6kw cooker 32A, sockets 32 A x2, Lights 6A, Smoke Alarm 6A. What would be the maximum demand on this?

Thank you, appreciate the help.
 
Not sure about the other circuits but for a cooker radial it is the first 10 amps plus 30% of the rest plus another 5A if there is a socket outlet in the control unit. Think lighting is 66% , but the consumer unit must be able to take the total without diversity being applied
 
Last edited by a moderator:
Hey.

Maximum demand is calculated as follows.

Lighting - 66% of the total current demand i.e add up all the lamps on your circuit and take 66% of that number.

Power - 100% of first ring circuit i.e 32A + 40% of all of all other ring circuits

Cooker - first 10A + 30% of the full load of the appliance over 10A + 5A if there is a socket outlet on the control unit.

If it's an instantaneous boiler then assume 100% demand,
also if its thermostatically controlled then there is no diversity allowable so you assume the current rating of the appliance

Shower - no diversity allowable

Hope this makes sense.
 
Last edited by a moderator:
As far as im aware, the maximum demand is the total amperage of all circuits after diversity has been taken into account.
Hope this helps...
 

Reply to Diversity and maximum demand confusion! in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock