Today was one of the worst I've had in 30 yrs in the trade. Got a call from a Coroner asking if I could attend an 'incident' as there was a need to ensure electrics were safe.
When I got there I was informed a husband had been carrying out some DIY and had been electrocuted. The body was still where he had died so I had to wait a while before I could go in.
His wife and family were all there...in bits obviously....What do you say to them?....I did my best and then just headed upstairs to sort it out. The family were refusing to leave the house so I had to make safe and get power back on.
Unfortunately as soon as I saw what the guy had been doing I'm ashamed to say I began to feel a little less sympathetic. Between the small kitchen and lounge was a small lobby,and he'd cut a LV downlight in the ceiling....on the wall was a new surface switch.
Upstairs a section of chipboard floor was up....he'd connector blocked the 2 lighting 1.5's and cut into the cooker feed which passed through the joist...it was clear he was planning to splice into the cooker cable with his light feed. What killed him was he had only turned off the ring main mcb......so either way he was planning to feed his light unfused off either the 30a ring or the 40a cooker. Also running through the joist were a couple of copper pipes....I suspect he may have been in contact with them while attempting to remove the insulation from a live cable.
I've stated on here before that I do not believe in regulating home electrics and I still believe that....you can just as easily kill yourself doing DIY building...the moral is if you dont know what you are doing, dont do it.
When I got there I was informed a husband had been carrying out some DIY and had been electrocuted. The body was still where he had died so I had to wait a while before I could go in.
His wife and family were all there...in bits obviously....What do you say to them?....I did my best and then just headed upstairs to sort it out. The family were refusing to leave the house so I had to make safe and get power back on.
Unfortunately as soon as I saw what the guy had been doing I'm ashamed to say I began to feel a little less sympathetic. Between the small kitchen and lounge was a small lobby,and he'd cut a LV downlight in the ceiling....on the wall was a new surface switch.
Upstairs a section of chipboard floor was up....he'd connector blocked the 2 lighting 1.5's and cut into the cooker feed which passed through the joist...it was clear he was planning to splice into the cooker cable with his light feed. What killed him was he had only turned off the ring main mcb......so either way he was planning to feed his light unfused off either the 30a ring or the 40a cooker. Also running through the joist were a couple of copper pipes....I suspect he may have been in contact with them while attempting to remove the insulation from a live cable.
I've stated on here before that I do not believe in regulating home electrics and I still believe that....you can just as easily kill yourself doing DIY building...the moral is if you dont know what you are doing, dont do it.
shame