Just about to Install a 50kW system. The DNO have asked to witness the commissioning of the system.

Can someone give me an idea of what they would expect on the day?
 
If you have applied under G59/2 expect them to check the warning stickers are in the right place and check the system shuts down when the power is cut. All in all not much for £750!

Tom
 
The DNO can ask you to carry out any test they wish for instance.

Under and over Frequency
Under and over voltage
Loss of mains
Vector shift

If you have not carried out any testing previously or you do not have the test equipment, I would recommend getting a consultant to carry out the testing for you. Hope this helps
 
Can strongly recommend SolarTest for on-site commissioning assistance, they're very well known by all the DNOs and senior assessors around the country. Most 3rd party testing houses charge around £500 for on-site commissioning and take around 4hrs on average apparently. The test equipment itself can cost around £11K to buy if you were to do it yourselves. I'm not 100% au fait with the exact nature of the tests but I'm sure Princesolar has it pretty much covered in his post above.
 
It is not something you can do yourself without that very expensive test kit !
We used to use a company from the reading area for the G59 relays and testing when needed , their blokes were mostly South Africans and were worth the money just for the stories of home, alone !!!
Who's your DNO , as we found that if you could provide proof of G59/2 compliance for the inverters then that was enough to keep them at bay ?
 
I can recommend a company called DEIF (UK). They're a large company that specialise in power geneation controls and have a G59/2 protection relay in there product range. They also sell a "ready built" G59/2 Protection Panel that you can install easily in many locations. They have experienced test engineers that will perform a witness test anywhere in the UK and as they produce the relays, they have great product knowledge. Have a look at www.deif.com.
 

Reply to DNO Witnessing commissioning of a G59/2 Installation 50kW in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, looking for some advice or knowledge on DNO approval. I’ve gone to sign up for export with Octopus. On the application form they’ve...
Replies
2
Views
1K
Hi all I had my PV/Battery setup installed in May and since then all my excess PV is just fed back to the grid for free. When I initially tried...
Replies
1
Views
2K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
952
Hello Is it possible for solar panel monitoring to over state the actual power generated by the system? My friend’s 6.4kW system has generated...
Replies
3
Views
1K
I have a partially completed installation of solar PV. The panels and inverters are working fine and generating plenty of power (13kWp), but I am...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock