Discuss Do I need over current protection? in the Industrial Electricians' Talk area at ElectriciansForums.net
if it is a fixed load, you could dispense with overload protection, but still need fault (short circuit) protection
I understand with a fixed load there is no chance of overload, but surely the short circuit protection will automatically give overload protection anyway even if it doesn’t need it.
Am I missing something?
no.you could have. say, a 2.5mm cable (27A CCC) protected by a 50A MCB giving fault protection, but the 50A MCB will not provide overload protection to the cable.
Upstream of the soft start, yes, downstream, no the soft start should be programmed to limit the overload current, if not the soft start instructions must give you the data you need.
Just remember if it's machinery BS7671 is irrelevant.
OP isn’t in UK? (Correct me if I’m wrong) So BS7671 is irrelevant anyway.
You're right, I saw the flag under his name and saw the little Union Jack and thought it was the whole flag, not just the small bit in the corner!
IEC 60364 still applies in AUS/NZ though it is a local interpretation like 7671, as would IEC 60204-1 which isn't so local.
Hi guys, i'm working on some project, do i still need over current protection if i'm using a soft starter and do I still need circuit breaker for that motor???
The soft start should have your overloads built in it you just have to read the manual and set to probably 115% X the full load of the motor and YES you have to have a circuit breaker for the soft start and motor
Why would you set to 115% of the FLC for a soft start?
Normally you set overloads to the FLC for DOL etc.
Not sure about the soft start, but they are usually sized ( 5hp 10hp ) so you have to put all the settings in. As
for the 115% is in article 430-250 of the NEC motors rated at 1.15 service factor is 125% Dave in the US we are taught to use the FLA on the motor and multiply it by 125%. All other motors multiply them by 115% the only information we use off the nameplate is the HP then you go to table 430-32(a1) of the NEC and find your hp and that’s where you get your amperage for that motor not the amperage on the
[automerge]1567306941[/automerge]
for the 115% is in article 430-250 of the NEC motors rated at 1.15 service factor is 125% Dave in the US we are taught to use the FLA on the motor and multiply it by 125%. All other motors multiply them by 115% the only information we use off the nameplate is the HP then you go to table 430-32(a1) of the NEC and find your hp and that’s where you get your amperage for that motor not the amperage on the nameplate
Dave I get what your saying on setting them in a soft start because it doesn’t have the in rush current a standard motor does. I’m not an expert on soft starts so I could have misquoted thinking about it
There is a common misconception in the UK that overloads need setting at more than the FLC, but normally they should be set at FLC as they are designed so that they cope with the inrush fir that setting.
Hi guys, sorry I haven't really send all the details about this, I've attached a photo of the diagram that the manual says, It says to put thermal overload relay? plus fuse upstream the soft starter? I'll be using this for a pump, I've also attached the photo of the details of the pump. Thanks much for helping and responding!
It's a hangover from the old oil filled dashpots that were used for OL protection. These you had to have set at 100% FLC.
In regard to the OP, if the manufacturers state you need OL protection, then you need it. Maybe this model of SS doesn't have built in OL protection.
Fuse it (or use MCB) upstream of the starter to protect the equipment from short circuit, and use the overload to protect the motor from overload. You can use a combination MCCB for the complete protection provided it is of the correct type and is adjustable to the nominal motor current.
In the UK our regulations state that all motors above 0.37kW must have overload protection, I imagine your regulations will be similar.
Yes, but, remember BS7671 is irrelevant when it comes to machiney.
110.2,xi
Reply to Do I need over current protection? in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Hi everyone, 1st post here. I'm a DIYer looking for some advise please. I've got a blender/mixer from India which has decided to pack up. I've...
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...