Reaction score
60
What are peoples thoughts on this, should socket outlets in the general public areas be RCD/RCBO protected? I believe they do and have put them down as a C2 on a recent EICR but recently got a phone call to say it's a C3!
 
I'm not aware that the general public randomly plug in their own equipment into the sockets inside the pub.
Usually these sockets are for pub game machines and for cleaners
If you generally feel these sockets present a danger then C2
However if it's just a improvement C3 it.
Sockets upto 20 amps should be rcd protected unless a documented risk assessment has deemed it not necessary.
Cables buried in walls feeding these sockets may also need additional protection from an rcd.
My first thoughts are it's a C3 but that's without knowing all the variables such as do any sockets supply outdoor equipment, heaters or used for outdoors especially in summer
It then may sway to a C2.
 
Last edited:
with a pub if it has living accommodation above it and both the pub and the accommodation share a main supply it comes under part p nonsense.
if they have different supplies then part p doesnt apply.
Spent most of my career working on pub, cafe and restaurant refits.
I have seen many a good gaffer get into arguments with labc over this. always funny to watch.
Just check in case you do any work which is normally notifiable if it were in a house as i have seen builders refurbing pubs masquerading as sparks get pulled up by building control and the licensing committee when they have queried emergency lighting, cctv etc and asked who did the work and due to the part p nonsense subsequently get fined as they werent part of a scam. only seen it twice but a pain none the less.
 
The cables supplying them are less than 50 mm depth and I've started seeing a lot more people charging phones, laptops or tablets for kids. Personally I think there a C2 because of the above and more and more sites are starting to change there sockets for the ones with the USB charge outlets.
 
The cables supplying them are less than 50 mm depth and I've started seeing a lot more people charging phones, laptops or tablets for kids. Personally I think there a C2 because of the above and more and more sites are starting to change there sockets for the ones with the USB charge outlets.
To be honest I would C3 sockets domestically say for upstairs were sockets are generally not likely to be used for supplying outdoor equipment yet they can be multiple USB type so I don't see any relevance.
This is not domestic of course
 
To be honest I would C3 sockets domestically say for upstairs were sockets are generally not likely to be used for supplying outdoor equipment yet they can be multiple USB type so I don't see any relevance.
This is not domestic of course
We have the same issue with outdoor light fittings not being mechanically protected and wanting to put them on rcd/RCBO protection, it always gets knocked back.
 

Reply to Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
671
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock