If you choose to listen to these manufactures, they will not warrant there cables past 20 years.Some of the earth sleeving is green, implying it was done before around 1977, some if it green/yellow, though unlikely a lot of work done after.
Certainly there are a lot of good reasons for changing the board to a modern one, ideally an all-RCBO style (so each circuit has a combined MCB for over-current protection and an RCD for earth leakage protection):
While the cables are old they are PVC (not the horrible old VIR rubber) so if they are in good condition (insulation resitance high, no signs of thermal stress or rodent damage, etc) you can probably use them for decades more to come, and that reduces the decorating impact of an update.
- Any after 17th regs amendment 3 are metal to be fire-resistant
- An 18th edition board would have surge protection
- Anything in the last decade or so would have additional RCD protection against shock
However, it would be worth considering having all of the accessories like 13A sockets and light switches updated if they are getting on and any have switches that are a bit sticky in action or cracked, etc. Maybe not essential if they are still usable, but then it would all be tested as part of the board replacement as well.
True, but cars typically come with only a few years warranty but often last 10-20 if looked after!If you choose to listen to these manufactures, they will not warrant there cables past 20 years.
Wrong about the 18th edition board having surge protection....recommendation only, not a requirementSome of the earth sleeving is green, implying it was done before around 1977, some if it green/yellow, though unlikely a lot of work done after.
Certainly there are a lot of good reasons for changing the board to a modern one, ideally an all-RCBO style (so each circuit has a combined MCB for over-current protection and an RCD for earth leakage protection):
While the cables are old they are PVC (not the horrible old VIR rubber) so if they are in good condition (insulation resitance high, no signs of thermal stress or rodent damage, etc) you can probably use them for decades more to come, and that reduces the decorating impact of an update.
- Any after 17th regs amendment 3 are metal to be fire-resistant
- An 18th edition board would have surge protection
- Anything in the last decade or so would have additional RCD protection against shock
However, it would be worth considering having all of the accessories like 13A sockets and light switches updated if they are getting on and any have switches that are a bit sticky in action or cracked, etc. Maybe not essential if they are still usable, but then it would all be tested as part of the board replacement as well.
It is a requirement in many cases from 443.4, optional for other cases when either:Wrong about the 18th edition board having surge protection....recommendation only, not a requirement
True, but cars typically come with only a few years warranty but often last 10-20 if looked after!
Very true.However, if I bought a property such as this, I would definitely consider a rewire.
Totally agree but a single dwelling is still only a recommendation for spdIt is a requirement in many cases from 443.4, optional for other cases when either:
I can't imagine many households with less than £2k replacement-value worth of electronics these days when you look at appliances with electronic control, LED lighting, TV, PC, etc, so it is very hard to argue that the extra £50 or less on the SPD is "not justified".
- A risk assessment according to 443.5 says it is not merited (but few are really going to do the assessment as it needs lengths and types of HV and LV feed lines) or
- "single dwelling units where the total value of the installation and equipment therein does not justify such protection"
Now it is true that such mains-powered electronics should tolerate Category II level surges of 2.5kV and events beyond that are rare, but consumer electronics seems to get crappier every year... Also how long until manufacturers of RCD/RCBO say SPD must be fitted?