A

allybally69

Hi all,

I replace about 30 lights from 2D to led, I'm under this impression I don't need to issue a certificate for this as it's only maintenance, am I wrong because the company are now chasing for a certificate

Many thanks
 
Take a look at chapter 63. You can use a minor works for change of current using equipment. That’s assuming you’ve changed the light fittings.
 
Guidance suggests a minor works certificate may be issued ..

If the paying customer wants one, then do one
 
You are not wrong as it is like for like. However it is sage to at least offer a minor works and test Zs etc. I replaced 600 x 600 fluors for LED and found 89v on the earth just doing routine testing. Always wise to check imo.
 
Hi all,

I replace about 30 lights from 2D to led, I'm under this impression I don't need to issue a certificate for this as it's only maintenance, am I wrong because the company are now chasing for a certificate

Many thanks

I would issue a minor works certificate for each circuit worked on.
 