When wiring a domestic kitchen is ok to supply integrated appliances from 32A/ 2.5mm ring via 20A D.P. Multi grid Switches , using 2.5mm on out going side of switches to a 1 gang socket or spur ?
 
That’s how a lot of new builds are done. Although I think there’s a few on here who don’t like using 20A DP switches protected by a 32A ocpd.
 
When wiring a domestic kitchen is ok to supply integrated appliances from 32A/ 2.5mm ring via 20A D.P. Multi grid Switches , using 2.5mm on out going side of switches to a 1 gang socket or spur ?
Are you putting in a ring solely for the integrated appliances?
 
Some appliance manufacturers specify a 16a over current device. So if you are strictly following the M.I then putting the appliance directly on a 32a ring is not correct.
of course the appliance will work hardwired directly to the 32a ring and I have done this on occasion but technically it’s not correct unless fuses down to the correct rating
 
A grid switch set up is totally compliant. It’s just spurs off an rfc.... although branched off very close together within the same box.
As with any infused spur, you can feed a double socket... but not usually done in a kitchen environment... single sockets only.


The above is for a “standard” rfc 32A OCPD
 

Reply to Domestic kitchens in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
824
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
UK Strange
I am decorating our bedroom which only has 1 double socket in it. We have been using multiple gang sockets which are untidy and a trip risk, so I...
Replies
10
Views
509

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock