All/most of the LED commercial downlights we fit have drivers that only allow one 0.75mm 2 core flex. Mostly we have plug-in LCM boxes and can wire flex to the plug if it is an MF plasterboard ceiling we use Click-Scholemore flow connectors.
 
Looks like there are two sets of terminals, the other set under the cover on the left.
Feed in and feed out to the next fitting.
Really should have been made with an earth terminal.

It is not permitted for Class 2 items to have an earth connected to them.
 
It is not permitted for Class 2 items to have an earth connected to them.
I take the view that if you are looping in and out of fittings this is part of the circuit and should have a CPC and that where there is the final connection to a fitting not requiring an earth eg double insulated etc. it is permissible to use two core flex.
 
Did manage to find some small connectors. Used j501’s then t+e to the fitting with a small connector inside the cap. Lesson learned to not buy gash from screwfix o_O
 
Then why not two core flex from the J501 to the fitting?


I had flex in the van but just decided to take the earth to the fitting. Obviously not needed but just thought to myself it’s better being there than not. cover every possible problem
 
This was answered by Dillb in post #2.
My preference is a wagolite with either 221's or 224 lighting connectors.
 
They can have an earthed connection point (often referred to as a parking terminal) and can have a suitably insulated CPC pass through them.
Agree Spin - if I'm reading it correctly reg 412.2.3.2 says Class 2 shall have a protective conductor at the accessory.
 
So does that mean that this class 2 cheap screwfix light does not meet regs as it has made no cpc termination or allowance for terminating cpc within the enclosure.

412.2.3.2 Except where Regulation 412.1.2 applies, a circuit supplying one or more items of Class II equipment shall have a circuit protective conductor run to and terminated at each point in wiring and at each accessory.


NOTE: This requirement is intended to take account of the replacement by the user of Class ll equipment by Class I equipment.


All depends on how you interpret it.
It doesn't say how it should be "terminated at each point in wiring and at each accessory."
Unusual for the regs not to be clear...... Go figure......
 
As I have already suggested, the solution is to strip the CPC back so that it can be terminated outside of the enclosure.

The minimum CSAs of 2.5mm2 and 4mm2 are not applicable as the CPC forms part of a multi core cable.

There is no requirement in BS7671 for terminations to be made within an enclosure.
However there is a requirement for this CPC to be terminated at the accessory.
 
Go on then Westie, explain.
You get the hump when members disagree with you and don’t offer an explanation.
Put your money where your mouth is.
 
As soon as you strip the cpc back and put it outside the enclosure it is no longer contained within the cable sheath and hence Reg 521.10.1 would come into play.
 