Deleted member 26818
521.10.1 does not apply to a CPC which complies with section 543.
As already said, does not apply.521.10.1
If it applies, then we can’t have non-sheathed earthing or bonding conductors, unless they’re in conduit or trunking.Does.
Nothing says the whole of the CPC has to form part of a multi core cable.Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
I remember an old Rock Ashley catalogue that showed an accessory for junction boxes that added earth terminals outside the J.box to allow additional terminals inside.leave it unenclosed, just as we used to do with JBs.
Quite correct but your words are going to deaf ears.Reading 543, it's got "if the protective conductor is not integral part of a cable .. the cross sectional area shall not be less than 2.5mm". So I'm thinking that irky 50mm bit of 1mm we've stripped back doesn't comply with 543, so needs to comply with ... think I'd better get my coat.
I think if anyone has deaf ears, it’s you.Quite correct but your words are going to deaf ears.