Haha, a dream it may well have been, but I shall take a look.......
 
Last edited by a moderator:
Ha, haaaaaaaa......page 38, the naughty little devil...........he's ticked SELV and double insulation and quotes "I reconnected various bits of "double insulation" equipment with no earth fitted"
Hmmm I knew I'd picked that up somewhere....
 
Where does it say "sole means" for the tick sheet

I fully agree with what you are saying but we are not using it for the circuit just the accessible parts in this case.
So if a "DI" accessory is used it must be checked and recorded (ticked).

412.2.3.2 and the note, for me allow 412.1.1 and note, which allows a double insulated fitting/accessory to be used in an environment where general persons would come in contact with the fitting. If not then all the double insulated equipment sold as double insulated must be re-classed and earthed.
 
Where does it say "sole means" for the tick sheet

I fully agree with what you are saying but we are not using it for the circuit just the accessible parts in this case.
So if a "DI" accessory is used it must be checked and recorded (ticked).

412.2.3.2 and the note, for me allow 412.1.1 and note, which allows a double insulated fitting/accessory to be used in an environment where general persons would come in contact with the fitting. If not then all the double insulated equipment sold as double insulated must be re-classed and earthed.

It doesnt, here lies the problem.
 
412.2.3.2 and the note, for me allow 412.1.1 and note, which allows a double insulated fitting/accessory to be used in an environment where general persons would come in contact with the fitting. If not then all the double insulated equipment sold as double insulated must be re-classed and earthed.

The rest of the circuit relies on ADS mate! Who cares what class of equipment is fitted on the circuit, but if the circuit's protective measure is ADS then ADS is it's protective measure, not double or reinforced insulation! lol

410.3.3 says; In each part of an electrical installation one or more protective measures shall be applied, taking account of the conditions of external influence.

It doesn't say; One or more protective measures shall be applied to each item of electrical equipment
 
Last edited:
Hey D Skelton, Im changing my mind, ......Ok you install a new circuit with SELV down lights or classII fitting.......you tick the boxes in the top section to say that you've inspected the fittings and double insulation symbol is present, noe earth fitted and it is adequate for basic and fault protection....it would be obvious that the installation or final circuit relied on ADS as you would aalso tick the required parts in Fault protection...??
 
Take a look at the OSG sample SoI..it has a tick in the SELV box as SELV lights installed......
 
Where does it say "sole means" for the tick sheet

I fully agree with what you are saying but we are not using it for the circuit just the accessible parts in this case.
So if a "DI" accessory is used it must be checked and recorded (ticked).

412.2.3.2 and the note, for me allow 412.1.1 and note, which allows a double insulated fitting/accessory to be used in an environment where general persons would come in contact with the fitting. If not then all the double insulated equipment sold as double insulated must be re-classed and earthed.

yeah , you keep quoting the same regs and going round in circles.
and your last sentence was pretty daft and fanciful to be honest.
clearly youre not open minded to alternative explanations so just keep on as you were.
 
It also has 16mm earthing conductors on every type of installation! lol

In relation to my OP, this must be where it's coming from!!!

Yep, lots of confussing info..OSG & Part P Doctor ticking basic and fault protection
 
Look you cant say things like that, these are reference books and they are used as guides produced by the same people that produce the Regs.........to post 55
 
Hmmm, did some research on this at lunch time and some heavey weights on the IET forum seem to agree with you, so perhaps its open to interpretation:confused5:
 