i am doing work in a void property for the council, there are downlights installed into a wet wall ceiling in the kitchen ( put in by previous tennant ) they are wanting to keep, when going round each downlight the earths were chopped away so went round sorted them all but i am getting no earth still so where they have joined from the original light position they have probably not joined the earth, the lights are wired through conduit with earths and the conduits earthed, and theres an earth going up to the light at the switch, i was wanting the ceiling down to get to the joint at the original light position but doing that would probably burst the wet wall and they would have to put a new ceiling up, the niceic inspector for the housing said that you can take a 4mm bond from the pipes in the boiler cupboard in the kitchen to the lights to give it an earth is this ok to do ?
I would try and get a CPC from the lights to the switch position if at all possible but if you can't then a 4mm to a suitable point to get continuity would suffice.
A note on the certificate and labels on the DB and CPC to make it easier for future works would also be advisable.
An extraneous conductive part maybe used as a protective conductor as long as it satisfies regulation 543.2.6.
Note a requirement is that the pipework is an extraneous conductive part and the cross sectional area shall be large enough or equal to applying regulation 543.1.1 which is sizing of protective conductors.
Best off reading regulation 543.2.1 and 543.2.6
Reply to Downlight earthing For housing in the UK Electrical Forum area at ElectriciansForums.net
Hi All, I am currently in the process of building an extension and I need to purchase some led downlights for my kitchen but unsure how many I...
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...