Not been about lately very busy thank god. Just a quickie to see if this is norm in UK Got a drawing for new house wiring normal circuits protected by RCD, One of the feeds goes to the pool pump room which has a 16A dual pole MCB and another 30ma RCD. whats ya thoughts please
 
No need for 2 RCD's inline, there's no discrimination between the 2. That wouldn't be the norm here.

If one trips the other will trip if both same mA rating.
 
Ideally I'd feed the pump pool room in SWA, then feed that from MCB with the RCD as described in the pool room only
 
Redundant protection anyone?
Customers always test these hugely unreliable devices called RCD's according to manufacturers requirements don't they...
 
Reading back the OP again I'm baffled as to what is protecting the feed to the pool house and then what Is then being fed in the pool house


The swa Is not there, (I don't think) I'm just saying from choice I'd of fed the pool house in that to provide the mechanical protection not needing the RCD protecting it. Then RCD local.
 
I think the idea is to provide DP isolation in the event of a fault in the pool area. A perfectly sound engineering reason to me but then I didn’t swallow the regs book when they tried to force-feed me it.
 