Dear All
Got a board change to do where there is an incoming oil pipe.
Plastic tank with PVC covered copper pipe most of the way. Comes inside and its just copper coming up through the floor. Did an IR test and got 0.00 so it needs bonding ( as I understand it its got to be under 0.02 to not need bonding)
Problem is the pipe is only about 8 or 9 mm dia. and i cant find a small enough clamp.
Someone suggested either a P clip or strap banding but they dont seem very professional. what are people using please
cheers
dnjr
 
You can get Ezybond clamps but they only go down to 15mm from what I have seen. There are rumours these are not in compliance with BS951 but I believe the manufacturer has resolved this.
 
You can get Ezybond clamps but they only go down to 15mm from what I have seen. There are rumours these are not in compliance with BS951 but I believe the manufacturer has resolved this.
Hi Westward. Yep seen them but as you say dont go small enough. I cant be the only person needing to bond oil pipes. there must be something out there....
 
Hi - only thing I found was an earth rod clamp. It's 9mm and I recall drilling it out to 10mm and being very careful not to overtighten it.

9mm ( 3/8" ) Cast Earth Clamp - https://www.tlc-direct.co.uk/Products/TLEC.html

IMG_0798.JPG
 
over 0.22Meg means it's not extraneous and does not need bonding. if under that, a continuity test is required from pipe to MET. a reading below 1.0 ohms suggests that it is bonded through other services, e.g.water and may not need additional bonding.
 
over 0.22Meg means it's not extraneous and does not need bonding. if under that, a continuity test is required from pipe to MET. a reading below 1.0 ohms suggests that it is bonded through other services, e.g.water and may not need additional bonding.

Hi Teletrix
I thought it was 0.022M ( 22000 ohms)
over that dont bond under that and it needs bonding
I did a continuity test and got 0.06 ohms I had it in mind it had to be below 0.05 to be acceptable (GN3) could be wrong, its been a long day
I cant find either a oil pipe bond or a water pipe bond so getting worried and going belt and braces
 
that 0.05 figure has to be the most misquoted figure of all time. it's the max. resistance betweem a bonding cable and the pipe to which it is bonded. I.E the resistance across the bonding clamp from cable to pipe.
 
teach me to read first
IR was 0.00M ( as I understand it , if its below 0.02M then it needs bonding if its above 0.02M then no need. Think I meant to put Over 0,02 but typed under...
Am I right this time davesparks ?

Also including some clue as to the units is quite important, I didn't quite register that you used an IR tester and was thinking in ohms.

My opinion on this subject is not exactly in line with the popular opinion on the forum, I'm inclined to interpret the regulations as requiring incoming services that be bonded at point of entry.
 
I usually manage to fit a standard earth clamp to an oil pipe.

I've only been in the trade 14 years which know isn't as many as some on here, but I've never had an issue doing this either? I've always used Tenby ones I know some cheaper ones are a different shape so perhaps don't grip smaller things?
 
I still di t get why an earth clamp wont fit? Take a pic im intrigued, ps dont forget to affix bonding label to your clamp
Hi Suffolk
Standard clamps I have seen either have a sort of box section bit in the clamp which would wobble about on top of the pipe or have a 'U' shaped but with the clamp which is too big and straddles the pipe and band can't go tight enough. Honest. I've tried. ...
 
Some care required if you are planning to solder a heating oil supply line. From memory, soldering needs about 200C and the auto ignition point of heating oil is about that too. Just saying ...
 
1.do it when there's no oil in the pipe

2. clamp heat sinks on pipe to prevent the oil overheating. it needs to vaporise to ignite.
 
The oil will not ignite unless it reaches temperature where it vaporizes allowing it to mix with oxygen, liquids do not burn it will however act as a heat sink removing the temperature from the pipe.
 
The oil will not ignite unless it reaches temperature where it vaporizes allowing it to mix with oxygen, liquids do not burn it will however act as a heat sink removing the temperature from the pipe.
That's right, these fuels won't burn without air. It's my understanding the vapour point of heating oil is significantly below the melting point of solder. Again, just saying ...
 
That's right, these fuels won't burn without air. It's my understanding the vapour point of heating oil is significantly below the melting point of solder. Again, just saying ...
The flash point of heating oil depending on the type will be approximately half 200°C.
 
but how can it vaporise when it's confined in the tube?
It can expand but even if it did manage to reach flash point and vaporize it would still need a sufficient heat source to ignite. Highly unlikely but most things are possible especially if it started spraying from a joint due to the expansion. I personally would not try it.
 
I've used a length of 1.0mm bare copper before. Bind it in tight turns around the pipe and back on itself if necessary. Clamp over that, done right it'll fit tight.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South coast

Thread Information

Title
Earth bond clamp for oil pipe
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35
Unsolved
--

Advert

Thread statistics

Created
dnjr,
Last reply from
Deleted member 9648,
Replies
35
Views
17,176

Advert

Back
Top