Please confirm that it is a fuse (what size) that blows/ruptures and it is the one which protects the pump or is it for the water heater as well?
Does the van have a neutral-earth link in the consumer unit when supplied by the generator?
Has the problem with the pump just started - it was previously satisfactory? Or is this a new van being wired now?
Is the van's metalwork and metal pipework bonded to the consumer unit earth terminal?
Have you IR tested the final circuits to the main earth terminal?
Are you powering up from the generator or mains when fault happens?
Right heres where we stand now. The neutral earth link is at the rcd fitted to the on board generator. I have IR tested right back to it and discovered that when i disconnect the link the fault clears. Im not overly clued up on generators my co-worker normally does that side but unfortunately he is on holiday.
In response to marconi
Its a 16A inline fuse which protects the handwash and the pump. All IR readings previously taken were clear but this was prob due to rcd at db being off. Its an old welfare trailer and think there has been a combination of works done including replacing some parts on generator and a faulty handwash unit which was replaced and assumed to be the issue.
By removing the N-E link you are simply breaking the earth circuit in a different place and stopping it doing anything. I would expect that to stop the tripping, so that makes sense, put the link back and leave it in otherwise there is a serious shock hazard that the RCD won't protect against.
The fact a 16A fuse is blowing indicates a fault of very low resistance. This does not tally with the floating earth tail from the pump hovering around 70V, you would expect it to go up to full mains w.r.t. earth. It's unlikely that both the old and the new pump would have such a fault.
Please could you confirm exactly what the 16A fuse is feeding and how. Is there a water heater? Could its element chamber be in contact with the pump? If so, I'm more inclined to think the fault is in the heater, and some nefarious arrangement of metalwork is making the pump's earth pigtail its only earth connection too. The element L & N may be disconnected from the supply until the water flow / pressure switch closes, so an IR test with the pump not pumping might not show the problem up.
Its a bit of a crazy setup but I'll explain it best i can. The 16A fuse is in line on the live to a 3kw instant hot water handwash. The pump is fed from the solanoid valve on the handwash unit. The handwash is activated by a sensor which then sends power to the pump via the solanoid valve. The handwash unit is essentially just a small water heater with a tap coming off it. The pump and the handwash are seperate but just housed together in this metal casing
I think that:
1. There is an N-E conductor link at the CU from N in to the CU MET. Thus all van wiring N and cpc are connected together.
2. There is no bond between the CU MET and van metalwork. The generator earth is connected to van metalwork someway. gernator earth is connected to MET.
3. Electric appliances are earthed back to MET but isolated from van metalwork. So cpcs are floating wrt metalwork. This changes when fly lead to pump motor connected. Keep reading...
4. If L and N incomer has been connected correctly to L and N terminals of the Main Switch/RCD of CU, then check next L and N connected correctly to CEEFORM plug at the generator (if there is one). If not, then check connected correctly to L and N as marked on generator.
5. With Ohmmeter check continuity between generator socket earth and generator casing. If there is continuity then next check between L and then N and to earth at socket. if socket Earth is not connected to generator casing check between L and N and generator casing. In either case it should only be N connected if at all.
6. If there has been a crossover of L and N at gennie, between gennie and CU or at CU, and there is a N-E link at generator but now effectively applied to L CU incomer, and the van metalwork is floating with respect to MET because of no bond to it, then when the earth fly lead is connected a short circuit via the fuse is put across the generator.
Or something like this. Easier to see if one draws it out.
Should also add when i disconnect the generator from the DB then everything tests out fine so i thought must be in the generator so I tried running a temp cable from the dist board to an alternative supply but then the short between live and earth comes back even with generator isolated
But what your saying makes sense there must be something reversed somewhere. Ive visually inspected all connections and everything appears to be connected correctly but havent put the meter on. Will try that now
Traced it back to a short between live and the motor casing in the generator. Disconnected motor to test it but couldnt find anything. Have since reconnected motor and fault has now cleared. No idea how and still none the wiser to the fault path it was taking to affect the pump etc. Thank you everyone for the help and hopefully i can repay the favour someday
Alternator casing?
Then, as Marconi points out, there must be a disconnection somewhere in the CPC / bonding arrangements. i.e. this was a multiple fault scenario. Otherwise the generator would have been permanently short-circuited as follows: Genny Line > machine frame > van structure > MET > N-E link > Genny Neutral. Something metal that the pump is in contact with, is not connected to that stud on the casing, e.g. the water pipe might be connected to the generator frame via the chassis, but not to the MET. You should find and fix this too, otherwise the next time a similar fault occurs, the fault path might include a human.
The pump is not really in contact with anything. The pipework is all flexible hose and its attached to the metal housing with rubber washers on a plastic base. The earth lead is the only thing connecting the pump with the rest of the metal work. Im going to keep hunting though to get to the bottom of it!
I might be missing something here but exactly how is the earthing in this mobile unit referenced because generators as far as I'm aware don't generate an earth
Nothing generates an earth, you just connect one side of your supply to it if you want to use its nice big handy equipotential (and then call that side the neutral). Within the van, if the supply is generated and used only on board, the only equipotential zone of interest is the van body, so that serves as the local 'earth', linked to neutral in the DB. If power generated on board runs outside, the whole shebang should be connected to a rod so that the ADS works outside too.
Reply to Earth fault on water pump in the UK Electrical Forum area at ElectriciansForums.net
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Dear Forum, I recently joined this forum, and writing for the first time. I like DIY activities, both for hobbies both to fix and repair stuff in...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
I have a submersed bore pump 85M down and covered by 40M water. The motor/pump is 1.1HP, capacitor run, 35uF in a capacitor box above ground, with...