Hello I’m a student learning about industrial wiring and circuits and we’re about to start learning about how to do loop impedance calculations. I have made a drawing of a three phase installation and was wondering if anyone could give me information on how I get the Ze Zs and R1 + R2. How would I do this with a three wire loop impedance meter and also how would I do it without one. Any help is appreciated, just trying to get my head round it first before we start the lessons. Photo is attached.
 

Attachments

  • D7714230-606E-4F61-A859-D85420B548C8.jpeg
    D7714230-606E-4F61-A859-D85420B548C8.jpeg
    267.8 KB · Views: 22
telectrix

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,171
Ze at the live side of the main isolator with earth disconnected, so isolator OFF. now you have a go at how to get R1+R2 and we cannthen see if you have ther right approach.
 
OP
J
Reaction score
2
Ze at the live side of the main isolator with earth disconnected, so isolator OFF. now you have a go at how to get R1+R2 and we cannthen see if you have ther right approach.
0.5ohm with earth disconnected and testing the earth back to the supply with the loop impedance meter. How do I get R1 and r2 and can you get it without a meter. Thanks
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,171
R1 is the phase conductor. R2 is the cpc. add them and get R1+R2, or short 1 end and measure in 1 hit. you need a meter set on continuity (low ohms). measure each phase-E. all 3 should be the same reading.
 
OP
J
Reaction score
2
Thanks for that so r1 and r2 is the same as Ze with a loop impedance meter or is R1 and R2 the part after the panel to the motor ? Thanks again it’s much appreciated
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,171
r1 and r2 (lower case) denotes end-end for a ring. important that you distinguish. you measure from isolator to control panel then from panel to motor and add them together.
 
OP
J
Reaction score
2
r1 and r2 (lower case) denotes end-end for a ring. important that you distinguish. you measure from isolator to control panel then from panel to motor and add them together.
What’s the difference from doing it with a loop impedance Meter then from a meter reading ohms ? Thanks
 
telectrix

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,171
,multimtercon ohmscand MFT on ohms should give same readings for R1 and R2 etc.. a multimeter can't measure Zs which is a live test.
 
OP
J
Reaction score
2
,multimtercon ohmscand MFT on ohms should give same readings for R1 and R2 etc.. a multimeter can't measure Zs which is a live test.
I think I understand now. I’ve attached my notes. I then add my r1 R2 reading to my Ze reading to get my zs? Does this all look correct ? Thanks
 

Attachments

  • 5B68CFC3-1CA4-4C41-8E23-793CE3E521A8.jpeg
    5B68CFC3-1CA4-4C41-8E23-793CE3E521A8.jpeg
    284.7 KB · Views: 7
telectrix

telectrix

-
Mentor
Esteemed
Arms
Reaction score
65,171
I think I understand now. I’ve attached my notes. I then add my r1 R2 reading to my Ze reading to get my zs? Does this all look correct ? Thanks
yes but please get into the habit or R1 as opposed to r1. etc. 2 entirely different measurements. in an exam you'd be marked down otherwise.
 