Is this an acceptable connection to an earth rod?

And is the water bond really necessary? (New duel RCD board recently fitted)
 

Attachments

  • 20200708_100123.jpg
    20200708_100123.jpg
    203.8 KB · Views: 716
  • 20200708_104603.jpg
    20200708_104603.jpg
    116.8 KB · Views: 198
Hi - that rod looks like it’s seriously rusted so I would not have used it myself. I doubt the clamp has made good connection through that rust, so for me it’s not ok.

Bonding to water may not be required if the incoming main is plastic and there are tests to confirm.
 
Hi - that rod looks like it’s seriously rusted so I would not have used it myself. I doubt the clamp has made good connection through that rust, so for me it’s not ok.

Bonding to water may not be required if the incoming main is plastic and there are tests to confirm.

Yes my thoughts exactly, A new board was fitted in April, and the earth/bonding cables upgraded, this is how it was done.

I've reconfigured some circuits in the property and have replaced this connection with a larger clamp, and have a Ze reading of 190 ohm. (Previously fluctuating to any number you want) And have brought the Zs readings down from 213 to 63.7
Will discuss with the client replacing for a new rod.

Incoming main is plastic, and I know they renewed the gas pipe only a year ago also.
 
Rod is too close to the building. try a new rod ( screwed togehter rods down to about 12 ft. surround rod with a bag of cat litter.
 
never seen a metal rod before i thought they were all copper? shocking job by the way
 