The sheet comes from an old UNEEDA guide on testing, it is an out of date publication but the table is still accurate. The formula can be found in GN8.Sorry where did this table come from ? and Richard where did the formla come from
95.0 is for 2 core, to say it will never be suitable is not correct.From what I can recall, the copper equivalence in conductance for 10mm2 doesn't kick in until you reach 95mm2 SWA?
By that that time you'll be wanting a conductance equivalence of 25mm2.
I just take it as read, that the armour of SWA, will never be suitable for bonding.
I had not heard this ... I look in BYB section 312.2.1 fig 3.9 where TNCS and PME seem to be the same thing (?).Not all TNCS supplies are PME but all PME supplies are TNCS so how do you know if it's PME, will the DNO always put a sticker on?
Quite simple.I see now, don't see relevance of question though.