Sorry where did this table come from ? and Richard where did the formla come from
The sheet comes from an old UNEEDA guide on testing, it is an out of date publication but the table is still accurate. The formula can be found in GN8.
 
From what I can recall, the copper equivalence in conductance for 10mm2 doesn't kick in until you reach 95mm2 SWA?
By that that time you'll be wanting a conductance equivalence of 25mm2.
I just take it as read, that the armour of SWA, will never be suitable for bonding.
 
From what I can recall, the copper equivalence in conductance for 10mm2 doesn't kick in until you reach 95mm2 SWA?
By that that time you'll be wanting a conductance equivalence of 25mm2.
I just take it as read, that the armour of SWA, will never be suitable for bonding.
95.0 is for 2 core, to say it will never be suitable is not correct.
 
Umm, in an Ice cream parlour at the mo, so don't have access to any books.
So can you tell me at what CSA Line conductors does 10mm2 for bonding stop being acceptable?
 
If I've understood correctly...
For TNS and TT - line conductor over 35mm bonding goes to 16mm, from table 54.7 and reg 544.1.1
For TNCS - DNO neutral conductor over 35mm bonding goes to 16mm, from reg 544.1.1 and table 54.8.
 
Not all TNCS supplies are PME but all PME supplies are TNCS so how do you know if it's PME, will the DNO always put a sticker on?
 
Not all TNCS supplies are PME but all PME supplies are TNCS so how do you know if it's PME, will the DNO always put a sticker on?
I had not heard this ... I look in BYB section 312.2.1 fig 3.9 where TNCS and PME seem to be the same thing (?).
 
Just what I've read elsewhere, so not sure, I think you might be right though.

I suppose you could have a on site Tx which TNCS supply with no multible earthing. So if no tx on site then the TNCS supply will always be PME?
 
Last edited:
TN-C-S is generally considered PME with some exceptions, the example you give could be one.
 
Page 47/48/49 of GN8 explain (and show) the difference between PME and PNB.
Daz
 
I see now, don't see relevance of question though.
Quite simple.
By the time the CSA of the armour is sufficient to offer the equivalent conductance of 10mm2 copper, you need the equivalence of 25mm2 copper.
As such SWA is never suitable for bonding.
 
Nope still don't know what you are getting at, armour can be used for supporting bonding.
 