Is anyone able to clarify with me how i can work out what earthing arrangement i have on site.

Supply comes into one of our motor switch rooms from an 11kv to LV transformer located directly outside. I can see 4 big copper bars (3phases and neutral) coming in which will then feed off to the Motor panels. There is an earth bar at the other side of the room which has various large earth cables connected.

There is one earth cable larger than the rest which i assume is the earthing supply cable and then the other slightly smaller ones i have traced which go to some of the bigger motors we have (100kw+).

Speaking to a few of the other guys (not electrical) and they said there are various earth spikes all over the site (may or may not be lightening protection). So would it be possible for our entire plant to be a TT or is it more likely that earth is derived from the neutral point of the hv transformer. Or is there an easy way to work this out

Thanks
 
Is anyone able to clarify with me how i can work out what earthing arrangement i have on site.

Supply comes into one of our motor switch rooms from an 11kv to LV transformer located directly outside. I can see 4 big copper bars (3phases and neutral) coming in which will then feed off to the Motor panels. There is an earth bar at the other side of the room which has various large earth cables connected.

There is one earth cable larger than the rest which i assume is the earthing supply cable and then the other slightly smaller ones i have traced which go to some of the bigger motors we have (100kw+).

Speaking to a few of the other guys (not electrical) and they said there are various earth spikes all over the site (may or may not be lightening protection). So would it be possible for our entire plant to be a TT or is it more likely that earth is derived from the neutral point of the hv transformer. Or is there an easy way to work this out

Thanks
It is the transformer earth. (at the mains position)
 
^^ Agree with the above. TNS. There will be a N>E link somewhere.

There will also be rods to reference the transformer star point to ground. (This is not TT).

Unless the star point is linked to the HV earthing system. However this isn't very common.
 
Is anyone able to clarify with me how i can work out what earthing arrangement i have on site.

Supply comes into one of our motor switch rooms from an 11kv to LV transformer located directly outside. I can see 4 big copper bars (3phases and neutral) coming in which will then feed off to the Motor panels. There is an earth bar at the other side of the room which has various large earth cables connected.

There is one earth cable larger than the rest which i assume is the earthing supply cable and then the other slightly smaller ones i have traced which go to some of the bigger motors we have (100kw+).

Speaking to a few of the other guys (not electrical) and they said there are various earth spikes all over the site (may or may not be lightening protection). So would it be possible for our entire plant to be a TT or is it more likely that earth is derived from the neutral point of the hv transformer. Or is there an easy way to work this out

Thanks
Dave you mention that you had a neutral bar in the gear what is all the ground cables connected to
 

Reply to Earthing arrangement in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
489
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
Replies
12
Views
2K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
449
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
394

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock