Discuss Earthing arrangement in the Electricians' Talk area at ElectriciansForums.net
Is anyone able to clarify with me how i can work out what earthing arrangement i have on site.
Supply comes into one of our motor switch rooms from an 11kv to LV transformer located directly outside. I can see 4 big copper bars (3phases and neutral) coming in which will then feed off to the Motor panels. There is an earth bar at the other side of the room which has various large earth cables connected.
There is one earth cable larger than the rest which i assume is the earthing supply cable and then the other slightly smaller ones i have traced which go to some of the bigger motors we have (100kw+).
Speaking to a few of the other guys (not electrical) and they said there are various earth spikes all over the site (may or may not be lightening protection). So would it be possible for our entire plant to be a TT or is it more likely that earth is derived from the neutral point of the hv transformer. Or is there an easy way to work this out
It is the transformer earth. (at the mains position)
^^ Agree with the above. TNS. There will be a N>E link somewhere.
There will also be rods to reference the transformer star point to ground. (This is not TT).
Unless the star point is linked to the HV earthing system. However this isn't very common.
Dave you mention that you had a neutral bar in the gear what is all the ground cables connected to
Reply to Earthing arrangement in the Electricians' Talk area at ElectriciansForums.net
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Hi All, I have a question trying to understand earthing arrangments SO, We have a DNO Substation, 4 Core armoured Feeding the Distribution Board...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...