Hi just after opinions on this one got three 3 phase supplies all 25mm 4 core swa, armour not been used for earth would you run a seperate 16mm earth for each supply or just loop all the earths from 1 16mm all the supplies are right next to each other
 
Why cant you use the armour?

You've got 3 cables all running to and from the same locations?
If they were all running to different places, i'd say 1 x 16mm each...
It doesn't seem enough... but then 3 sounds like too much.
Go for 2 x 16mm:rolleyes:
 
it's 3 small boards all.next to each all fed from the same main distribution board just not sure whether I'd get away with the 1 earth going to an earth block and then to each board
 
If you have correctly sized the main earth for the 3 phase supply to the main board, the surely you should use the same sizing formula for sizing the main earthing conductors to the remaining 3 sub main distribution boards, after all commonsense rules OK.
 
Hi - a 16mm for each and you probably don't need to look further, but otherwise few questions to help clarify -
Installation means of earthing?
Are sub boards having the same earthing design? Incoming conductor size?
Bonding requirements?
 

Reply to Earthing for 3 phase boards in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
337
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
439
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
637
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock