Discuss Earthing for CU Change. in the UK Electrical Forum area at ElectriciansForums.net
SKY
Starting to 2nd question myself before doing my Part P inspection - have 2330 L2 and L3 plus 2392 and 17th edition.
I have lots of commercial experience with big industrial machines and motors but I do fall down on domestic.
The CU change I have booked is a PME install, under 17th edition I understand that I have to connect to the main water pipe and the main gas pipe using 10mm cable (after checking).
On other install I have done I have connected the earth from an earth terminal next to the meter - PME does not have this.
So
I'm guessing that the main earthing conductors are connected inside the CU on the earth bar and then feed out to the gas and water pipe?
Thanks All
You can use the earth bar in the CU as the MET or put an external one in, really up to you.
As for 10mm main bonding, if there's 6mm in place and there's no sign of damage, overheating, arcing etc you could get away with it if it entails a lot of work putting new stuff in.
you could fit your own MET near the CCU
Or do you mean that there isnt a earth connection point for TN-C-S at the suppliers overcurrent protective device were is the existing earthing conductor connected ?
the adiabatic at P 160...543.1.3 will calculate this....
A couple of main points aswell Sky, the earth clamp needs to be within 600mm of the gas/water incomer (or as close as physically possible). The bonding conductor needs to be one complete length without any terminations (apart from in the met internal or external of the board.
Good luck with your assessment and go to bed, its late :).
LOL: off to bed now - Thanks for all for the advise.
Water service I can get right after the stopcock - the gas is underground and pops up close to the main water service stopcock so will pick it up there.
Hoping that the ELECSA guy will be happy with that as I can't do much more than that!
If both incoming services are next to one another like you say, you can use one earth cable for both. On the second clamp remove the sheath to terminate to the screw on the clamp without cutting the wire.
Hi paul
and before any branchwork also
yes its late so why you still up lol
Mate i am turning into a insomniac
especially with this JOB I am doing for me bruvs getting sleepless nights lol over it
unlike my bruvs which is within 600mm but after a water filter 1cm copper pipe then a Plastic Tee
I used the wander lead yes its 0.02 at the pipe side of the clamp but before the Tee and on the other outlet of the tee about 80ohms
I hate plastic pipework and fittings
People forget that water is a poor conductor and pure H2O is an issolator. Think car batteries?
I'm off to bed, up in five hours, on a new project I'll pm you tomorrow brucelee.
Reply to Earthing for CU Change. in the UK Electrical Forum area at ElectriciansForums.net
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Morning guys, Just been to look at a CU change and there was a bit of an oddity with the PME connection in the old black cut out. Looking at the...