hi all

just wondering what is the best way to earth my shed.

The shed is the full metal type which they sell at screwfix 8ft x 6ft

I've put a single light inside and one outside from fused connection units inside the shed, they run from another fcu which is a RCD FCU from my decking.

so what's the best way to earth the shed as it's fully metal
 
As the shed is not part of the electrical system it will not require earthing.
If the shed is intended to create an equipotential zone inside it and the shed is tested to show it is introducing an earth potential into this zone then it would require bonding.
This would require a (probably) 10mm² green and yellow single core cable run from a connection to the shed itself back to the main earth terminal in your consumer unit and continuity of the cable and the connection to the shed proved.
 
As the shed is not part of the electrical system it will not require earthing.
If the shed is intended to create an equipotential zone inside it and the shed is tested to show it is introducing an earth potential into this zone then it would require bonding.
This would require a (probably) 10mm² green and yellow single core cable run from a connection to the shed itself back to the main earth terminal in your consumer unit and continuity of the cable and the connection to the shed proved.
,

I would install a garage board in shed and TT the shed As 9/10 there is not a 10mm bonding conductor from MET to shed location and running one would be difficult compared to driving a couple of coupled earth rods in.
 
48? still a teenager.

haha. You are just prehistoric though mate.

upload_2016-9-17_11-2-35.png


:)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk
Business Name
DBelec

Thread Information

Title
earthing metal shed
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Dan Brown,
Last reply from
Spoon,
Replies
11
Views
14,077

Advert

Back
Top