All "extraneous conductive parts" should be bonded to your earth anyway, this means metallic service pipes or steelworks that are in contact with the true Earth. This applies to any supply system as you want to avoid finding an appliance with metalwork on one CPC system being at a different voltage to something else you can touch on another.

In the UK at least you are not allowed to rely on a water pipe as a means of earthing, basically because it can be changed at any time by a plumber or the water supply company and it will likely be replaced by plastic (or plastic joint) so it may become un usable and by folks who know little of, and have no requirement to, deal with electrical aspects.

So while you might have a fantastic earth due to a long length of private metal pipe, you probably should add a dedicated rod and that would be the basis for designing your system if TT. Basically on a TT system you measure the rod Ra, if that is low enough to be stable (UK regs below 200 ohms) that can then be used to select means of fault disconnection. almost always a RCD (or RBCO) as you are very, VERY unlikely to have a rod able to trip a 32A MCB or whatever.


No, if the CPC is linked to the supply neutral by a wire it is TN.

If those wires are separate at source it is TN-S, if there is only one wire (N & CPC) then it is TN-C

It is only if your CPC system is only linked to the supply through the Earth itself by means of a rod, buried foundations, etc, that you have a TT system.


I'm not sure I quite understand what you are proposing. More worryingly, I'm not sure you understand it either!

Trying to have a mixed earthing system seems to me to be a recipe for disaster if something goes wrong on the supply side, then TN-C objects go live and you could be touching that along with a true Earthed TT object from another circuit.

If it were me (who knows a bit about what I am doing) I would try to make it a bit like a UK TN-C-S arrangement where you treat the supply meter box as TN-C, then you split for TN-S (as the DNO does here) along with additional earthing and bonding of water pipes on the CPC from that point. Within your CU I would put existing TN-C circuits NE on N bar & L from MCBs, and migrate as many as you can, as quickly as practical, to 3-wire TN-S using L & N off RCBOs and the CPC to the E bar.

On this forum we cannot condone attempting work beyond your capabilities as this appears to be. Replacing a CU really is a job for a professional electrician, none of us want to hear of a fatal accident as a result.

However from what you currently have, and if that is representative of "professional" work in many cases, I can see you are between a rock and a hard place. In your situation it might be worth looking at attending a courses to learn a bit more and get some advice, or trying to find local help if they are better than whoever did this. At the very least you need to have some test tools to check stuff before you switch it, and to check it really is dead before you try to work on anything (i.e. safe isolation). A proper voltage tester / continuity tester is a critical thing to have for safe isolation. Also some half-decent socket tester, etc.
Thanks
The one thing I did do when we bought the house was to go around bonding things.
 
All "extraneous conductive parts" should be bonded to your earth anyway, this means metallic service pipes or steelworks that are in contact with the true Earth. This applies to any supply system as you want to avoid finding an appliance with metalwork on one CPC system being at a different voltage to something else you can touch on another.

In the UK at least you are not allowed to rely on a water pipe as a means of earthing, basically because it can be changed at any time by a plumber or the water supply company and it will likely be replaced by plastic (or plastic joint) so it may become un usable and by folks who know little of, and have no requirement to, deal with electrical aspects.

So while you might have a fantastic earth due to a long length of private metal pipe, you probably should add a dedicated rod and that would be the basis for designing your system if TT. Basically on a TT system you measure the rod Ra, if that is low enough to be stable (UK regs below 200 ohms) that can then be used to select means of fault disconnection. almost always a RCD (or RBCO) as you are very, VERY unlikely to have a rod able to trip a 32A MCB or whatever.


No, if the CPC is linked to the supply neutral by a wire it is TN.

If those wires are separate at source it is TN-S, if there is only one wire (N & CPC) then it is TN-C

It is only if your CPC system is only linked to the supply through the Earth itself by means of a rod, buried foundations, etc, that you have a TT system.


I'm not sure I quite understand what you are proposing. More worryingly, I'm not sure you understand it either!

Trying to have a mixed earthing system seems to me to be a recipe for disaster if something goes wrong on the supply side, then TN-C objects go live and you could be touching that along with a true Earthed TT object from another circuit.

If it were me (who knows a bit about what I am doing) I would try to make it a bit like a UK TN-C-S arrangement where you treat the supply meter box as TN-C, then you split for TN-S (as the DNO does here) along with additional earthing and bonding of water pipes on the CPC from that point. Within your CU I would put existing TN-C circuits NE on N bar & L from MCBs, and migrate as many as you can, as quickly as practical, to 3-wire TN-S using L & N off RCBOs and the CPC to the E bar.

On this forum we cannot condone attempting work beyond your capabilities as this appears to be. Replacing a CU really is a job for a professional electrician, none of us want to hear of a fatal accident as a result.

However from what you currently have, and if that is representative of "professional" work in many cases, I can see you are between a rock and a hard place. In your situation it might be worth looking at attending a courses to learn a bit more and get some advice, or trying to find local help if they are better than whoever did this. At the very least you need to have some test tools to check stuff before you switch it, and to check it really is dead before you try to work on anything (i.e. safe isolation). A proper voltage tester / continuity tester is a critical thing to have for safe isolation. Also some half-decent socket tester, etc.
Thanks, I appreciate your advice.
One of the first things I did when we bought the house was to go around bonding things as best I could. (water pipes, metal sinks ect). Basically, the electrics here are @hite, and I've had a few shocks, zaps or whatever you want to call non fatal electrical tinglings?
I have a reasonable understanding, but as stated I'm no professional. I do have the basics like a multimeter to check if something is live, but none of the expensive kit like earth testing meters ect.
The thing here is, that all of the sockets ect are supplied with two core cable. Neutral and earth are combined from the fuse box on. I'm planning to totally rewire and whilst I originally thought t was a TN-C supply due to the N+E linking at the fuse box, it seems there's no earth other than what might be supplied at the transformer which is over a Km away (The source cables are single core L+N and no not neutral sheaved with earth btw). So I really suspect I need a more local earth? I understand the UK situation with water pipes, but chances are mine won't be changed for years and if they were I'd certainly know as we have a two acre plot in a very rural location. I have an earth rod, but it's a single 5/8th one I bought out from the UK to service a shed rather than a whole house, so the water pipe, though not unacceptable in the UK seems a better option here in rural BG?
Whilst the split box sounds weird, I may have not explained it very well. I can't put the circuits that have combined E+N through an RCB protected system, but the circuits that I rewire as TT will require it. As it stands at the moment, all the wiring goes through a couple of old fashioned ceramic fuses and then into 16a MCB's. That's fine to protect cables, but does nothing to protect me! My thinking is to migrate separate circuits as I rewire across to the RCD protected side as I go.
I know that confusing two earthing systems is not great, but short ripping the whole lot out in one go (I wish!) I'm not sure it can be helped?
I'm a rubbish at explaining my thinking as the wiring is in this house.
PS .... I totally understand nobody wants to hear that some --- has zapped himself to death because of what's been said on here. Thanks
 
Thanks, I appreciate your advice.
One of the first things I did when we bought the house was to go around bonding things as best I could. (water pipes, metal sinks ect). Basically, the electrics here are @hite, and I've had a few shocks, zaps or whatever you want to call non fatal electrical tinglings?
Bonding exposed metal objects (those with any sort of electrical function, and service pipes) together is a very good start and was common practice in the UK before RCD became cheap and ubiquitous.
I have a reasonable understanding, but as stated I'm no professional. I do have the basics like a multimeter to check if something is live, but none of the expensive kit like earth testing meters ect.
A multimeter is better than nothing, but make damn sure it is at least CAT-III rated to 300V so it won't explode in your face if you make a mistake like trying to measure volts on amps range, etc.

However, multimeters are frowned upon for safely and reliably detecting if something is live because they can do so many jobs, and some of those might also have a fuse that can be blown and you don't realise it. A simple mistake that can be fatal is checking for AC volts on the DC range and seeing only a fraction of what is there. Conversely, they are often around 1M ohm impedance so they can should voltages due to capacitive coupling that are not significant.

That is what the simple voltage testers are worth getting. they do one basic job reliably, and draw 2-3mA to light the LEDs so don't show the "phantom voltages" that multimeters report. As they can be had for £10 on Screw fix it is worth getting one and using as your main test. But always check your tester works before (and ideally after) checking something is not live. A quick check on a known good socket or similar (some show 12V so even car battery will do) should light it up and then your next test is better proven.

The thing here is, that all of the sockets ect are supplied with two core cable. Neutral and earth are combined from the fuse box on. I'm planning to totally rewire and whilst I originally thought t was a TN-C supply due to the N+E linking at the fuse box, it seems there's no earth other than what might be supplied at the transformer which is over a Km away
That is your earth! And that is why TN-C installations (supply) normally have multiple earths added at various points for reliability.
(The source cables are single core L+N and no not neutral sheaved with earth btw). So I really suspect I need a more local earth? I understand the UK situation with water pipes, but chances are mine won't be changed for years and if they were I'd certainly know as we have a two acre plot in a very rural location. I have an earth rod, but it's a single 5/8th one I bought out from the UK to service a shed rather than a whole house, so the water pipe, though not unacceptable in the UK seems a better option here in rural BG?
Use both. The pipe should be bonded anyway and likely will be VERY good, but another rod will not do any harm. Just be careful where it is driven in!
Whilst the split box sounds weird, I may have not explained it very well. I can't put the circuits that have combined E+N through an RCB protected system, but the circuits that I rewire as TT will require it. As it stands at the moment, all the wiring goes through a couple of old fashioned ceramic fuses and then into 16a MCB's. That's fine to protect cables, but does nothing to protect me! My thinking is to migrate separate circuits as I rewire across to the RCD protected side as I go.
I know that confusing two earthing systems is not great, but short ripping the whole lot out in one go (I wish!) I'm not sure it can be helped?
It seems you are either confused by the two types, or are going to try and mix-and-match within one installation which is a very bad idea.

Going from TN-C to TN-C-S is a fairly simple step, as the CU using MCBs is fine for the N+E of existing circuits and what you are doing it having a known safe and reliable N-E link before the CU (UK practice [*]) and as peossible you separate out N+E of final circuits so you can put those N & L on RCD/RCBO protection.

To go TT safely you must have all circuits CPCs isolated from the N, otherwise it has additional risks you don't currently have.

[*] In the USA they link N&E inside the first/main panel/CU as they often have "two-wire" supplies like you see, though in practice 3 wires as 120-0-120V. Sub-panels are then separate N & E routes so 3/4 wire.
I'm a rubbish at explaining my thinking as the wiring is in this house.
PS .... I totally understand nobody wants to hear that some --- has zapped himself to death because of what's been said on here. Thanks
Above all take care and never assume anything, verify! And get help/advice as far as you possibly can.
 
the source cables coming into the fuse box, where the neutral is horribly combined with all the neutral lines coming in from plugs and lights

OK. This terminal stud is really what defines the setup and it is a pretty standard feature of Soviet-era installations. If one of the two incoming single-core cables is connected to it, that cable (the supply neutral) is deliberately being used to earth the fuse box chassis and therefore hopefully anything else that is supposed to be earthed. That makes it a TN-C or TN-C-S system, or at least it should.

From that point onwards, loads and circuits might have their earths connected three different ways:
a) Using a 2-core cable with one combined core from that stud serving both neutral and earth: TN-C
b) Using a 3-core cable with two separate cores from that stud serving neutral and earth: TN-C-S
c) Not connected back to that stud, but to a separate rod: TT

Mixing circuits (a) and (b) on the same system isn't itself dangerous. One wants as many (b) as possible because they can be RCD protected and are inherently safer than (a) even without RCD. Mixing circuits (c) with either (a) or (b) is dangerous in itself, before anything is even switched on, because of the risk of the rod earth being at a different potential to the incoming CNE.

If you trawl pictures of Soviet panels on the WWW, you will find plenty of examples of the CNE terminal stud or bar with umpteen cables attached, looking insecure and often on the brink of failure through overheating or just falling off. Paradoxically, it's the one point at which you really don't want a bad connection on TN-C systems as loss of continuity causes supposedly earthed bits to become live.

If any of the above is not 100% clear and obvious, I'd suggest some further detailed study in the principles and practice of earthing before tackling any alterations. One could make things worse rather than better.
 
Last edited by a moderator:
OK. This terminal stud is really what defines the setup and it is a pretty standard feature of Soviet-era installations. If one of the two incoming single-core cables is connected to it, that cable (the supply neutral) is deliberately being used to earth the fuse box chassis and therefore hopefully anything else that is supposed to be earthed. That makes it a TN-C or TN-C-S system, or at least it should.

From that point onwards, loads and circuits might have their earths connected three different ways:
a) Using a 2-core cable with one combined core from that stud serving both neutral and earth: TN-C
b) Using a 3-core cable with two separate cores from that stud serving neutral and earth: TN-C-S
c) Not connected back to that stud, but to a separate rod: TT

Mixing circuits (a) and (b) on the same system isn't itself dangerous. One wants as many (b) as possible because they can be RCD protected and are inherently safer than (a) even without RCD. Mixing circuits (c) with either (a) or (b) is dangerous in itself, before anything is even switched on, because of the risk of the rod earth being at a different potential to the incoming CNE.

If you trawl pictures of Soviet panels on the WWW, you will find plenty of examples of the CNE terminal stud or bar with umpteen cables attached, looking insecure and often on the brink of failure through overheating or just falling off. Paradoxically, it's the one point at which you really don't want a bad connection on TN-C systems as loss of continuity causes supposedly earthed bits to become live.

If any of the above is not 100% clear and obvious, I'd suggest some further detailed study in the principles and practice of earthing before tackling any alterations. One could make things worse rather than better.
Thanks, I get what you are saying and it makes sense.
 
Hi, Hope you dont mind me adding a further question to this thread.
I am a retired NCB electrician, not domestic qualified. I have a house in Bulgaria, it has been rewired and has the following installation.
Supply is roadside box with a pair of 50a MCB to two core overhead cable to the house & a neighbour. I assume (always an issue) its TN-C as both supplies have N connected to busbar which is also bonded to box chassis.
The house installation is all 3 core with CPC wired to CPC busbar in a modern CU.
The CU has separate N & CPC busbars and uses MCB's on each circuit.
All internal pipework is plastic from supply to each sink/bathroom, no extraneous metal fittings
No external earth is provided.
Advice please;
Should I replace all MCB's with RCBO's or RCD's ?
Bond CPN to N busbar in CU ?
something else ?

Thanks
Steve