P

paul_sut

Hi all i did a fuse board change the other day and when testing i got a ZE reading of 0.43 and a KA of 5.93 why would the KA be so high, also zs failed on all circuits for breakers. This is TNS. what would any one recommend??
 

Murdoch

Regular EF Member
Messages
26,648
Location
Woking
Are you sure your KA is correct?
 
OP
P

paul_sut

i've just got one of these new megger mft1710 and i pressume i have i think it came up 593A? also why would my zs fail for example for the ring 32a breaker i got 6.29??
 

Murdoch

Regular EF Member
Messages
26,648
Location
Woking
i've just got one of these new megger mft1710 and i pressume i have i think it came up 593A? also why would my zs fail for example for the ring 32a breaker i got 6.29??
In red - are you sure? Your OP said 5.93Ka - which is it?

Your ring may have a problem, what were your "dead" tests like? Or is it all circuits?
 
OP
P

p11jor

Loose connection somewhere in the original install? I had a zS of 4000 once!

There is a few fixes tho, you could add some bonding to create parallel paths, this may bring your zs down

You could rewire it with a bigger CSA cable to lower the r1+r2 value

Or as you will now have rcd protection you can have a maximum of 1667ohms but if it's over 200ohms check it out!
 
OP
P

p11jor

Just another thought if you were taking the Ze then the main earth would of been removed from the earth terminal, once that was replaced to start doing zs's could the terminal screw cross threaded and backed off abit?
 
OP
P

paul_sut

All rcd protected now but is old house all decorated etc dont want disturbance if you know what i mean. main bonding all done to water and gas 10.0mm, main earth 16.0mm to sheath. Another reading i got was the boiler which was new circuit tight connections etc and the zs was 6.41 on 16a breaker.?
 

Murdoch

Regular EF Member
Messages
26,648
Location
Woking
Hum, not sure what's going on here. Silly question but you did reconnect the earth to the CU/Met didn't you?
 
OP
P

paul_sut

yea i thought this aswell checked all connections all ok and tight
 
OP
P

p11jor

Mmmmm wierd one, has the whole wiring been inspected?? I.e is the ring final results ok? It could be a case of a DIY job few jbs spuring of the 2.5 in 1mm Somthing on the lines of that?
 
OP
R

Rauer

Check the main earth connection , then get onto the supplier, least that's what I'd do!
 
OP
R

Rauer

Hasnt that ze failed too tho? Daily certain a tns is 0.18
 

telectrix

Disrespected Scouser
Electrician's Arms
Trainee Access
Messages
63,525
Location
cheshire/staffordshire
try measuring Zs at the outgoing of MCB. if its higher than the Ze, then it's the MCB and/or main switch affecting the value.
 
OP
P

paul_sut

Thanks for all your help i think im gonna arrange a re visit as this baffled me, yea all r1 r2 and end to end good on ring all good. but again how far do i go as obviosly only priced for fuse board one of these things i suppose.
 

jumpin jax

Regular EF Member
Messages
308
Location
East
Ze for tns is max 0.8, have you checked your loop readings on your meter with your known monthly check source to check meter ok
 

Murdoch

Regular EF Member
Messages
26,648
Location
Woking
With the Zs readings you refer to makes me wonder if the CU is reliant on parallel paths to gas and water for the "earth" path. Are you sure that the main earth is connected from the CU to MET to incoming supply??

What was the Ze for the old board? i.e. before you started?
 
OP
R

Rauer

TN-S max. Ze is 0.8.
My bad! Why I have 0.18 in my head I don't know!
As someone said in an earlier post you've got additional protection in (rcd ) so aslong as its not too bad it's ok .........ish
 

Jimmy Boy

Electrician's Arms
Messages
1,281
Location
Lounge
Hi all i did a fuse board change the other day and when testing i got a ZE reading of 0.43 and a KA of 5.93 why would the KA be so high, also zs failed on all circuits for breakers. This is TNS. what would any one recommend??
Don't suppose you got a Ze and PFC before you whipped the old CU out ?
J
 

jumpin jax

Regular EF Member
Messages
308
Location
East
Try a loop test on the mcb at the board, it could be the main RCD or main switch causing bizarre loop readings causing bizarre loop readings
 
OP
P

p11jor

Just go as far as you have done and put it in lim on schedule of inspections (I think you will be covered anyway due to building fabric and floor covering) and just make good use of the departures section, cover yourself as much as you can.
 

Murdoch

Regular EF Member
Messages
26,648
Location
Woking
OP
R

Rauer

One of my old employers used to change my measured zs's to calculated ones from r1+r2 as his assessor used to query them if they were different and he told him he would prefer it that way!!
 
OP
P

p11jor

I would do another Ze too....could be the armoured knocked when brushing up cable clippings from the meter cupboard, loosened it off abit
 

Murdoch

Regular EF Member
Messages
26,648
Location
Woking
but again how far do i go as obviosly only priced for fuse board one of these things i suppose.
Next fuseboard change estimate you do you, should include a caveat, stating that if you identify issues with the installation, which is very likely, that additional costs are to be expected.
 
OP
P

paul_sut

No unfortunatly i didnt do test on old board. ring reading for excample were l=0.36 n=0.36 e=0.56 r1 r2=0.93 then zs 6.29
Main earth def connected straight to sheath of cable and connections all tight.
 
OP
P

paul_sut

Il try the zs on outgoing of mcb next time thank you again
 
OP
P

p11jor

What reading was you getting from the main earth to the gas and water?
 
OP
P

paul_sut

never tested between earths i will try this on nxt visit to what do you think may have happened?
 