Hi all i did a fuse board change the other day and when testing i got a ZE reading of 0.43 and a KA of 5.93 why would the KA be so high, also zs failed on all circuits for breakers. This is TNS. what would any one recommend??
 
i've just got one of these new megger mft1710 and i pressume i have i think it came up 593A? also why would my zs fail for example for the ring 32a breaker i got 6.29??
 
i've just got one of these new megger mft1710 and i pressume i have i think it came up 593A? also why would my zs fail for example for the ring 32a breaker i got 6.29??

In red - are you sure? Your OP said 5.93Ka - which is it?

Your ring may have a problem, what were your "dead" tests like? Or is it all circuits?
 
Loose connection somewhere in the original install? I had a zS of 4000 once!

There is a few fixes tho, you could add some bonding to create parallel paths, this may bring your zs down

You could rewire it with a bigger CSA cable to lower the r1+r2 value

Or as you will now have rcd protection you can have a maximum of 1667ohms but if it's over 200ohms check it out!
 
Just another thought if you were taking the Ze then the main earth would of been removed from the earth terminal, once that was replaced to start doing zs's could the terminal screw cross threaded and backed off abit?
 
All rcd protected now but is old house all decorated etc dont want disturbance if you know what i mean. main bonding all done to water and gas 10.0mm, main earth 16.0mm to sheath. Another reading i got was the boiler which was new circuit tight connections etc and the zs was 6.41 on 16a breaker.?
 
Mmmmm wierd one, has the whole wiring been inspected?? I.e is the ring final results ok? It could be a case of a DIY job few jbs spuring of the 2.5 in 1mm Somthing on the lines of that?
 
try measuring Zs at the outgoing of MCB. if its higher than the Ze, then it's the MCB and/or main switch affecting the value.
 
Thanks for all your help i think im gonna arrange a re visit as this baffled me, yea all r1 r2 and end to end good on ring all good. but again how far do i go as obviosly only priced for fuse board one of these things i suppose.
 

Reply to Earthing Reading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
769
Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
431
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
969
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock