With the Zs readings you refer to makes me wonder if the CU is reliant on parallel paths to gas and water for the "earth" path. Are you sure that the main earth is connected from the CU to MET to incoming supply??
What was the Ze for the old board? i.e. before you started?
What was the Ze for the old board? i.e. before you started?