Knobhead

Having done industrial work all my life I’m struggling with the idea of only earthing one end of a SWA. To my mind the more earth paths the better. All the plants I’ve worked on would be steel framed so you have a huge parallel network to start with. All the plants came under the M&Q regs so all power circuits would be tested 6 monthly. A minimum of .5 for the earth return was required but .01 would be the norm.
To most of you guy’s domestic earthing arrangements are second nature, to me earthing just one end of the armouring negates a good earth path. The only time I’d do anything like it would be for instrument cables to prevent circulating currents.
 
Just completed a TT install to an outbuilding. SWA earthed at supply end and a fresh TT install at the new building complete with dedicated rod and incoming water on copper pipe....However with inspection intervals at 10 years (if at all for domestic) I feel safer knowing the addition I have done will stand alone by itself quite safely.
 
So in a TT installation what happens when the outer serving gets damaged say near the supply end and the armouring rust away? You have a cable with a metallic sheath not earthed. Why can’t the cable be earthed at both ends utilising both the earth rods. I can’t see the problem with parallel paths. I’m not suggesting the neutral be earthed at the secondary point.

GH as you say the water at the remote end was earthed to the remote spike, isn’t that a parallel path. OK you could introduce a short section of plastic. So far to me it seems madness.
 
Last edited by a moderator:
that's a special case -if it's a conversion to TT for outbuildings

armour can't be connected 'load' side
 
Last edited by a moderator:
Its down to the probability of introducing differing earth potentials in the system, not just getting the best possible earth. Commercial installations are normally under the control of a competent/skilled person and usually inspected & tested by the book every 5 years. Domestics on the other hand tend to be regarded by the owner as "imortal" and if they dont get a belt (luck or not) will normally disregard the recomendation on 10 yearly inspections. Therefore by keeping instals simple you should negate the possible problems when things start to go wrong.

For SWA to degrade to a state where the armour no longer protects the cable is going to take decades. Even if the armour at the gland fails, the remainder should be intact providing a degree of protection to the cable. If installed correctly it should be burried deep enough to prevent spade damage with the addition of warning tape/tiles above....
 
6 months in acidic soil and a cable armouring will rot through.
As for voltage differential, if the two spikes are linked how are you going get one?
If it happens that the bonding between the rods is severed, there’s still protection at both ends.
The copper water pipe puzzles me, it’s bonded at both ends? It also forms a part of your ground earth network.

It really makes no sense to my industrial brain.
 
Last edited by a moderator: