Chaps,
I'm after a bit of sensible advice (I know I might have come to the wrong place
) but I'm not posting this publicly because the company in question could be on the forums in the arms.
So the backstory is I was approached by a landlord, she'd had an EICR carried out on a rental through the agency that manages the property for her. These are the issues they found:-
1. Damaged 2 gang socket in living room - C2
2. Smoke alarm head missing in attic (base fitted connections accessible to touch) - C2
3. Consumer unit not fireproof - C3
4. Installation not protected by a surge protective device - C3
5. Incorrect cable identification in attic smoke alarm - C3
6. Earth bonding to water not verified due to kitchen units - FI
This cost her £90 and they were there about 2 hours from what I can gather.
To fix the C2's and investigate the water bonding, they've quoted £130.
To fix the C3's (supply and install a new 18th edition consumer unit with surge protection) £450.
She wanted a second opinion... these are my views based on visiting the place this morning.
1. Hairline crack in the face plate, not severely damaged, no exposed live parts. I'm torn on this one, yes it could deteriorate with use, but based on location I'd say it doesn't get much. But it should be replaced just in case, so on that basis I think I'd C2 it.
2. This is at ceiling height, and the connections in question are a base mounted terminal block. You'd have to make a conscious choice to reach it and work hard to actually touch the connections in question. But this problem goes away once the detector head is installed, which leads me onto the fact that the detectors are 3 years past their replacement due date.
3. This is an absolute crock. It's a split load board, mounted in the downstairs toilet which is by the front door. So if you were to come down the stairs (which do not run above the downstairs loo), you'd have two options... the front door or the back. In my opinion this should not be listed.
4. Now my understanding is, C3 means it's a non-compliance that would significantly improve the safety of the installation if corrected. Do I think this should be listed??? Hell no. I wouldn't list the lack of an SPD under any classification.
5. As best as I can tell... this is the neutral missing some blue sleeving. They've clearly not removed the other smoke detectors (as they would have picked up the replacement date being past due) but the one I removed was also lacking complete sleeving. Is adding this going to significantly improve the safety of the installation??? I don't think so, so should it be listed as a C3? No I don't think so, just like I wouldn't classify missing switched live identification.
6. This is a doozy
Their reasons for not verifying I guess are the fact they would have had to open the door of the cupboard under the sink to... can you guess... reveal the incoming pipework and the fact there is no bonding clamp or any evidence of a clamp ever being present... just as there is no evidence of a cable being present in the consumer unit. I did IR from MET (with main earth and gas bond attached) and got 0.47Mohm at the incoming pipework. It's a blue plastic incomer, none of the radiators or pipework in bathrooms that I tested showed a value less than this, so as best as I can tell it doesn't need bonding.
Anyhow, comments and thoughts welcome
I'm after a bit of sensible advice (I know I might have come to the wrong place
) but I'm not posting this publicly because the company in question could be on the forums in the arms.So the backstory is I was approached by a landlord, she'd had an EICR carried out on a rental through the agency that manages the property for her. These are the issues they found:-
1. Damaged 2 gang socket in living room - C2
2. Smoke alarm head missing in attic (base fitted connections accessible to touch) - C2
3. Consumer unit not fireproof - C3
4. Installation not protected by a surge protective device - C3
5. Incorrect cable identification in attic smoke alarm - C3
6. Earth bonding to water not verified due to kitchen units - FI
This cost her £90 and they were there about 2 hours from what I can gather.
To fix the C2's and investigate the water bonding, they've quoted £130.
To fix the C3's (supply and install a new 18th edition consumer unit with surge protection) £450.
She wanted a second opinion... these are my views based on visiting the place this morning.
1. Hairline crack in the face plate, not severely damaged, no exposed live parts. I'm torn on this one, yes it could deteriorate with use, but based on location I'd say it doesn't get much. But it should be replaced just in case, so on that basis I think I'd C2 it.
2. This is at ceiling height, and the connections in question are a base mounted terminal block. You'd have to make a conscious choice to reach it and work hard to actually touch the connections in question. But this problem goes away once the detector head is installed, which leads me onto the fact that the detectors are 3 years past their replacement due date.
3. This is an absolute crock. It's a split load board, mounted in the downstairs toilet which is by the front door. So if you were to come down the stairs (which do not run above the downstairs loo), you'd have two options... the front door or the back. In my opinion this should not be listed.
4. Now my understanding is, C3 means it's a non-compliance that would significantly improve the safety of the installation if corrected. Do I think this should be listed??? Hell no. I wouldn't list the lack of an SPD under any classification.
5. As best as I can tell... this is the neutral missing some blue sleeving. They've clearly not removed the other smoke detectors (as they would have picked up the replacement date being past due) but the one I removed was also lacking complete sleeving. Is adding this going to significantly improve the safety of the installation??? I don't think so, so should it be listed as a C3? No I don't think so, just like I wouldn't classify missing switched live identification.
6. This is a doozy
Their reasons for not verifying I guess are the fact they would have had to open the door of the cupboard under the sink to... can you guess... reveal the incoming pipework and the fact there is no bonding clamp or any evidence of a clamp ever being present... just as there is no evidence of a cable being present in the consumer unit. I did IR from MET (with main earth and gas bond attached) and got 0.47Mohm at the incoming pipework. It's a blue plastic incomer, none of the radiators or pipework in bathrooms that I tested showed a value less than this, so as best as I can tell it doesn't need bonding.Anyhow, comments and thoughts welcome