What is the right code for:

a) central heating pipes running directly below a socket (left to right). Could heat from the pipes slightly warm the socket and possibly warm a flex cord of a plugged in appliance if it touches the pipe?

Would lagging the pipes solve this?

b) electric cable crossing under 22mm gas pipe on wall. (less than 25mm distance).

One reason for the min 25mm distance is to avoid damage to cables if work is done on the pipes (e.g. blow torch). But this would not be immediately dangerous. Is there another reason for needing a gap for a cold pipe?
 
Woth clarifying The BS7671 does not give maximum distances of accessories and wiring from pipe work but gives regulations for proximity of wiring to other services
 
a) picture as requested.

I don't think 40mm is close enough for heat from pipes to affect the sockets but the power cord from the fcu is touching one pipe.

So, opinion on code? I think C3 unless the heat could damage the power cord?

One answer might be to box in those pipes but it still might be an issue with the power cord from a plug being bent too much at the bottom where plugged in over the boxed part.

EICR CODE too close to pipes picture - EletriciansForums.net
 
I always mark things like this such as a socket right next to radiator etc as a c3 referencing the schedules 5.19 suitability of accessories for external influences

And things like cable touching pipes etc as c3 5.2 cables correctly supported throughout their run.

That way you're not saying its dangerous and needs changing right away but if anything were to happen you've covered your ---.
 
a) picture as requested.

I don't think 40mm is close enough for heat from pipes to affect the sockets but the power cord from the fcu is touching one pipe.

So, opinion on code? I think C3 unless the heat could damage the power cord?

One answer might be to box in those pipes but it still might be an issue with the power cord from a plug being bent too much at the bottom where plugged in over the boxed part.

View attachment 49786
This is considerably better than some of the drawings I have received for jobs in the past. Bravo
 

Reply to EICR CODE too close to pipes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock