has this company been informed of this?
How are they changing the certificate? Striking out what they don't like and writing in their version or producing a new certificate?
Who's signature is on the revised document, and are they aware of it?
No one has actually amended the certificate. The agent emailed me and said the C2s aren’t correct so they’ve downgraded. No new paperwork has been issued.
 
What does the electrician who issued the EICR think of this novel "downgrading"? I must say if I received news such as that as an issuer I would take it up with the local building control.
 
What does the electrician who issued the EICR think of this novel "downgrading"? I must say if I received news such as that as an issuer I would take it up with the local building control.
Unfortunately I have no way of contacting the original electrician. I would if I could!
 
If you have the full EICR, they should all be on there.
How many pages do you have?
 
Sadly it just says the company name which employs a large number of electricians so I am unable to speak to the individual.
Well, you go to the company. They will know which electrician was sent to your property.
 
I take it this is the company that issued the original and not the 'modified' version.
There should be a signature there, but I'm sure that the company would be interested to know that someone is changing the certs that they issued and put their signature to.
 
I take it this is the company that issued the original and not the 'modified' version.
There should be a signature there, but I'm sure that the company would be interested to know that someone is changing the certs that they issued and put their signature to.

OP stated that cert hasn't been changed. The issue is a management company deciding that advice from their own electrical experts means no action needs to be taken in regard to the report's findings.
 
I take it this is the company that issued the original and not the 'modified' version.
There should be a signature there, but I'm sure that the company would be interested to know that someone is changing the certs that they issued and put their signature to.
They haven’t actually amended the certificate. They have just said they won’t action the issues.
 
The other acceptable alternative would be for the letting agents electrical experts to contact the original firm and to argue it out with them, to try to get them to amend the certificate. We all know that no two testers will come up with identical EICRs, so if the agent thinks the C2s should be C3s, then they should convince the original tester.
 
My issue isn’t with the individual that carried out the EICR
I know it’s not.

But if I issued or I was the owner of a company than one of my employees issue an EICR and had someone state it is wrong and refused to rectify the issues i would want to know.

I would be a bit miffed. I’d have strong words with letting agent and then report them to local building control / authority.

id remind them the max fine for this is now £30,000.00.
 
I think BPG 4 suggests a C2 for this.
The regs have required this for nearly 15 years now, much longer than the requirement for domestic lighting circuits to have rcd protection (which bpg 4 suggests is a C3) so the two things aren’t entirely equal in one sense.
15th Edition 1981, Amended June 1987.
Reg 471-47. 35 years.
Screenshot_20220227-031614_Gallery.jpg
 
They haven’t actually amended the certificate. They have just said they won’t action the issues.
Have they said this in writing, if so ask when they will be issuing the revised EICR, because at the moment you have an EICR that requires remedial action within 28days of its issue date, if they refuse your next port of call is building control.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EICR downgraded by Landlord’s Agent from C2 to C3
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
71

Thread Tags

Tags Tags
agent eicr

Advert

Thread statistics

Created
LauraCanning,
Last reply from
Simon47,
Replies
71
Views
7,696

Advert