Difficult to suggest a price without knowing how much experience you have of doing EICRs because this would be a factor. If you are in competition with others and you go in at £15+ per circuit you will not stand a chance but don't go for a competitive price if you are going to run a loss.
 
you need to spend an hour or so, looking at the 9 boards. are all circuits Identified? covers off, are they a rat's nest? once you've seen the state of it, discuss with client on how thorough an inspection they want. based on the above, then estimate time taken to test/inspect and write it all up, then give them a price.
 
Going in blind...nothing available..probably never been tested since install which I reckon was about 30 years ago.
I don't think I'd personally use sampling as an option. So looking like a full inspection and test required really.

I'd do as suggested by Tel, get the covers off the boards and see just what you're up against before submitting a quotation.
 
I think one thing I would need to know in pricing is how accessible are the DBs for testing. In the way that often there are things you cannot turn off or limited times as to when you can. With the fact that it may be 30 years old, and no test certs (can't imagined how they got away with that) I would be doing 50% sampling minimum increasing on the more faults/damage seen and take into account GN3 guidance on that. I normally work on £20-£30 per circuit. I also usually offer a discount on the EICR if the remedial work is done by me. In this way it is possible to offer a good discount as the remedial work can carry an uplift to reflect the reduction.
 