Block of flats, 3 phase incomer split to feed 3 flats, PME coming in with a 16mm earth. This then feeds a 60a switched fuse that feed the flat. The cpc leaves the switch fuse as 6mm and then clamps to the armouring of a 10mm 2 core swa that goes up 2 floors to the flat db. At the flat db 4 strands of the armouring are then used for the cpc.

I have 2 questions that I'm unsure of. 1. What size would you record on the eicr for the earthing and 2. What would you code the 4 strands of armouring being used at the db? C2?

Any thoughts?

Thanks
 
my opinion

C2 and C2 to both

is the arnouring being used as the main bonding contctor to the incoming services within the flat ?
 
i would also mention this on the EICR as the main bonding should be assessed on the incomming neutral size
 