Discuss EICR testing and inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Before anyone asks I am a qualified spark.. been off the tools for years and getting back into it..
In regards to EICR’s it’s been a while..
Acceptable to add R1 R2 to Ze for ZS or do you all test all 3 anyway? I know it’s not acceptable to ZS and take off ZE to get R1 R2..
 
measure R1+R2 or R2 so you can stick something in the colummn. i usually do R2 with a wander lead to the faceplate screws, (saves taking faceplates off ). then measure Zs where practical (socket adapteror/ rose cover off). educated guesses can fill any blank boxes.tin hat on.
 
I prefer calculating Zs. And if I do I don’t then measure it as well.
If rfc end to end measurements are spot on and the CU is a complete rats nest I might occasionally measure Zs on the rfc at several strategic points, especially spurs if they are identifiable. But only after checking it’s a ring.
 

Reply to EICR testing and inspection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
997
OLDBOY
O
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
823
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
598
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
802
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock