A 40A MCB should be able to run all day at the current he is getting. I still think something is spiking it, either a switch or contactor. Have you tried setting the clamp on "Max" and see what you get as the unit clicks on and off?
 
Thanks for all that info.

I did check all connections when I initially looked at the boiler and all are tight including the c/u end. I also looked at the circuit board inside the boiler and found no signs of overheating. I did check the resistance of the elements and found that two of them were around 19 ohms and the third being around 20 ohms so didn't think there was anything wrong.

I will have a look for this adjustment screw though with a view to turning it down a tad. Will try another 40amp mcb to see if that makes a difference as well.

But now that we have all this sunny weather the tenant won't have it on any way so it'll be October time 'hopefully' when it will get the chance to trip again.

cheers to all for you input.
 
cant you upgrade mcb 45A on 10mm cable
Hager don't seem to do 45 amp mcbs. Next up is a 50 amp which am not keen in using as cable is run between floors where there is a possibility of insulation.
Not keen on mixing mcb makes in c/u. Have heard the manufacturers don't warranty them in a different make of board.
 