I understand what you´re saying but on the other hand I´ll get peace of mind that the earthing system is up todate and effective.
well then apply for a PME connection then....yes, its a more reliable means of earthing....what eng was getting at was if there was any extranious in that garage/outbuilding then you would`v had to extend the equepotential zone with a length of 10mm CSA g/y...
dont forget as well that you may want to upgrade any main bonding in the house if you go for TN-C-S....
definately if less than 6mmCSA
 
rods more cost effective here eng....and if he gets it right with them.....

Nothing to stop him including the outbuilding earth rods into the PME earthing system. In fact it is preferable and will make any new PME system that much safer, if ever a neutral fault developed on the system, especially if he gets nice low Ra values on those rods!! lol!!
 
Nothing to stop him including the outbuilding earth rods into the PME earthing system. In fact it is preferable and will make any new PME system that much safer, if ever a neutral fault developed on the system, especially if he gets nice low Ra values on those rods!! lol!!
yep...good backup eng...
in fact...i distinctly remember a few days ago...we had a TN-S with a rod....the O/P disconnected the rod therefore creating an extranious conductive part right next to the head....
from what i remember you advised him to reconnect...pronto...
 
yep...good backup eng...
in fact...i distinctly remember a few days ago...we had a TN-S with a rod....the O/P disconnected the rod therefore creating an extranious conductive part right next to the head....
from what i remember you advised him to reconnect...pronto...


Yes, ...I remember that too ...lol!!
 