YTSOxford

Hi all...
I'm helping to wire a newly built garage that is detached from the main house. The garage is 2story, and the bloke is going to use the upstairs as an escape from his family, pool table, sky tv, bar etc. The upstairs is having a firedoor and being fully plastered as is the ceiling of the lower floor.

So, for the fused spur for a door motor, should this be surface mounted to the ceiling in a patress box??? Flush mounting, with metal K/O box would look neater, but is this a problem with the fireproofing of the ceiling????
Thanks all!
 
Consider this, why does the isolator have to be near the motor?

Route conduit along ceiling - inline with backbone for neatness, from motor unit. Take conduit to a fused spur unit mounted on a wall to suit client's need. Pull 3 core flex through conduit, and terminate into replacement end.

No openings in fire rated ceiling.
 