OP
Knobhead
Drive references,
All the panels I worked on once we got rid on the open slate panels would be draw out starters. We would keep spares of these to hand. If you couldn’t repair a draw in situ you would get a spare and fit that. The internal wiring was numbered the same be it a 0.5HP drive or 150HP. Bigger drives were hard wired in the cubical.
View attachment 11273
It was the cubical that had the drive reference. I worked on kilns so the first reference would be the kiln number. Second reference the tier in the panel working from the left (a letter). Third reference was the cubical number from the top.
So for a cubical on kiln 2, 3[SUP]rd[/SUP] tier, 4[SUP]th[/SUP] cubical down the reference would be K2/C/4/ followed by the wire number.
View attachment 11274
All the panels I worked on once we got rid on the open slate panels would be draw out starters. We would keep spares of these to hand. If you couldn’t repair a draw in situ you would get a spare and fit that. The internal wiring was numbered the same be it a 0.5HP drive or 150HP. Bigger drives were hard wired in the cubical.
View attachment 11273
It was the cubical that had the drive reference. I worked on kilns so the first reference would be the kiln number. Second reference the tier in the panel working from the left (a letter). Third reference was the cubical number from the top.
So for a cubical on kiln 2, 3[SUP]rd[/SUP] tier, 4[SUP]th[/SUP] cubical down the reference would be K2/C/4/ followed by the wire number.
View attachment 11274