No not Boots.
Forgive my ignorance Tim, but in what circumstance would you use a contactor for emergency lighting, as I've seen a few new installs recently where one is installed next to the control mcb and ctu for emergency lighting. I hadn't the opportunity to look behind the covers yet, but my understanding was it was switching the emergency lighting. One unit had only 4x NM em lights and when I tested through ctu the contactor pulled and em lights came "on."I'm a little confused why you think you need a contactor to switch an 80W load (20 x 4 watts ) that draws 0.34 amps
My comments were based on installations I've seen in England and Wales and I've never encountered the system you describe which others have now explained is common in Ireland and sometimes in other places too. So best to disregard what I said!Forgive my ignorance Tim, but in what circumstance would you use a contactor for emergency lighting, as I've seen a few new installs recently where one is installed next to the control mcb and ctu for emergency lighting. I hadn't the opportunity to look behind the covers yet, but my understanding was it was switching the emergency lighting. One unit had only 4x NM em lights and when I tested through ctu the contactor pulled and em lights came "on."
Hi Risteard,As mentioned it's done through a CTU (central test unit) and contactors rather than key switches.
I.S. 3217 are the Emergency Lighting Rules which need to be complied with - it's not BS 5266. It's done a bit differently.
I'm a little confused why you think you need a contactor to switch an 80W load (20 x 4 watts ) that draws 0.34 amps
There is a large retail chain in the UK doing this, one push button and a 3hr timer.
You see this is a good point.I've seen this sort of thing in a few places but can't work out how you are supposed to get around the whole building and check they are all working properly at the 3 hour point before the timer runs out.
Electric scooter?I've seen this sort of thing in a few places but can't work out how you are supposed to get around the whole building and check they are all working properly at the 3 hour point before the timer runs out.
Hi Dave,You do when the emergency lights are connected to different circuits but a single test switch in a central location.
Yes that's what it meansHi Dave,
By eml being connected to different circuits, do you mean if some eml's are coming off their local lighting mcbs?