I'm carrying out an inspection report certificate for emergency lighting for an HMO house. I have noticed that there are no emergency lights in the back dining area and kitchen. The electricians who fitted then, did so in 2013 only in the stair wells and front corridor leading to main door. I have suggested to the landlord that there should be emergency lighting in the back of the building also leading to the front. Am I right to suggest this as I feel I cannot issue an certificate for him. I admit I need more Education and knowledge on this type of works.
 
If you are providing a periodic inspection of the emergency lighting then you would need to define the deviations from the current standard on the report. This is not a case of pass or fail, it is a report on the installation at the moment. You cannot really refuse to issue the report because the installation does not meet the standards, that is the purpose of the report, to identify these issues.
If you have concerns then these can be raised in the report and then the landlord can decide on the action they wish to take.
If you are stating that the system does not comply with the current standards then you would have to classify the deviations in reference to the standards.
For a house as an HMO I would usually expect that the lighting you describe would be adequate, however if it is a very large building and the route from front to back is part of the escape route and has no borrowed light and there are changes in level and direction as well then additional lighting would be required.
It would be best to review the risk assessment for the property to ascertain why the system has been designed as it has, since this may clarify the reasoning behind the arrangement.
 
If you are providing a periodic inspection of the emergency lighting then you would need to define the deviations from the current standard on the report. This is not a case of pass or fail, it is a report on the installation at the moment. You cannot really refuse to issue the report because the installation does not meet the standards, that is the purpose of the report, to identify these issues.
If you have concerns then these can be raised in the report and then the landlord can decide on the action they wish to take.
If you are stating that the system does not comply with the current standards then you would have to classify the deviations in reference to the standards.
For a house as an HMO I would usually expect that the lighting you describe would be adequate, however if it is a very large building and the route from front to back is part of the escape route and has no borrowed light and there are changes in level and direction as well then additional lighting would be required.
It would be best to review the risk assessment for the property to ascertain why the system has been designed as it has, since this may clarify the reasoning behind the arrangement.
Most business people don't want to see deviations or a failed cert. They want to get there licence or insurance. He agreed to fit additional emergency lights as all his other properties are all fitted with the emergency lights where needed. My question is am I right, because this installation was done in 2015. On that date they should of fitted them.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
WEST MIDLANDS

Thread Information

Title
Emergency Lighting for HMO PROPERTY
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
sham,
Last reply from
Bellendian,
Replies
18
Views
10,042

Advert

Back
Top