Did the green charge indicator ever come on, if not the no power to PL. Is the test switch in test mode?

most I've fitted come with some charge in the battery but if these are totally dead then they may require some charging to function.
 
Did the green charge indicator ever come on, if not the no power to PL. Is the test switch in test mode?

most I've fitted come with some charge in the battery but if these are totally dead then they may require some charging to function.
So at the min the lights are switched by photocell and come on at night so the batteries should be charged and test mode does nothing
 
Fed via photocell too

The supply to the battery pack should be from the PL. When the test switch is in the test position then power is cut fooling the light into thinking a loss of power has occurred and the light should switch to battery back up. When not in the test position the batteries will charge indicated by, usually, a green led being lit.

The supply to the lamp, via the contactor and photo cell should be is the switched live and should go in the appropriate terminals on the light.
 
The supply to the battery pack should be from the PL. When the test switch is in the test position then power is cut fooling the light into thinking a loss of power has occurred and the light should switch to battery back up. When not in the test position the batteries will charge indicated by, usually, a green led being lit.

The supply to the lamp, via the contactor and photo cell should be is the switched live and should go in the appropriate terminals on the light.
Thanks understand a bit more now, I’m back tomorrow so will check the wiring cheers for your help
 
Go back to basics initially and check your incoming supply as per #22 it wouldn't be the first time a contactor ditches the PL, if the charge indication goes off when the contactor is off it is connected incorrectly but not necessarily at the fitting. If all this is okay you can probably assume the fitting/s are duff.
 