The installer should have confirmed the Ze (external earth loop) with the rest of the property off and earths disconnected. The fact that was all boxed in means this was not done
As a matter of urgency get the main gas and water pipes bondedm this way stray earth currents are likely to go through the bonding and not your boiler wiring loom
I would also suggest you contact the car charger manufacturer and ask them to send someone to asess the situation
I also noticed the EV installer appears to have installed a Hager RCD inside an Eaton unit- not good
As a matter of urgency get the main gas and water pipes bondedm this way stray earth currents are likely to go through the bonding and not your boiler wiring loom
I would also suggest you contact the car charger manufacturer and ask them to send someone to asess the situation
I also noticed the EV installer appears to have installed a Hager RCD inside an Eaton unit- not good