Is there any kind of pattern that could be weather related or length of run time related? If the worst comes to the worst and you can't pick any issues up visually or by testing you could split the circuit and see if you can localize the problem that way.
 
Is there any kind of pattern that could be weather related or length of run time related? If the worst comes to the worst and you can't pick any issues up visually or by testing you could split the circuit and see if you can localize the problem that way.

I'm thinking this is what I'll have to do. The weather has been wild of late, but the problem precedes the very stormy/wet weather. Any thoughts on a faulty ballast as a source of overload or am I clutching at straws?
 
A trick I've used before is to install a minature fuse holder at each fitting and fit a fairly close rated fuse. They're pretty cheap and you can use a panel mounted type and solder tails to it and insulate with some heat shrink over the top of everything. If it's a rogue fitting that's causing the tripping then the next time it happens it will be the only fitting that doesn't light due to the blown fuse.

images.jpeg
 
Marco makes a good point.

Or if you don't have time to do that, Could you not disconnect the circuit half way and see what happens the after a few nights?
 
It's really quick to install in most fittings if you pre-solder the tails before you go to site and go armed with a handful of Wagos or small sized chocbloc connectors.
 
Fit a transient voltage arrestor in each fitting, pennies each.
Could be killing the mcb when it switches off with voltage spikes, cheap fittings?
Seen it before and it made some mess of timeclock after timeclock till we nailed it. Timeclocks dont like 10kv.
At least the fittings are not from C.E.F.?


Boydy
 
Fit a transient voltage arrestor in each fitting, pennies each.
Could be killing the mcb when it switches off with voltage spikes, cheap fittings?
Seen it before and it made some mess of timeclock after timeclock till we nailed it. Timeclocks dont like 10kv.
At least the fittings are not from C.E.F.?


Boydy

Cheers for that ( and Marvo & Dillb too!), I was running out of ideas. Good few things to try.
The fittings are Phillips and are original to the build. The other half of the lights/building have been fine.
I normally quite enjoy fault finding, but this one is starting to grate.

Thanks again all for helpful contributions, much appreciated.
 
Not a lose or snagged cable I've found this before all ok and IR clear but on occasion it would trip.
Turns out it was the slightest nick on the incoming cable someone had caught the insulation and every now and then it would touch the metal case of the fitting.
Although you said conduit and the ones I encountered where flex and so guessing bit more freedom to move

Just a suggestion
 