The OP has been given the option to pm me with his phone number via a pm to him if he wants this done. If not, that is on his head. Lets list the things that we would look for before we reach for a reel of cable....
What earthing arrangement is it, bonding, rcd's??? Ze test, Zs on existing circuit whilst energized using a checkabox. In the cu see if its one or two cables on the mcb, end to end tests, R1+R2, IR test, is the mcb the correct ratting for the cable, is the cable the correct size for the load and the extra load? Now he can look at extending it (once we now if its a rfc or a radial).
Then all we have to do is install the new sockets within zones and within the part p regs, do most of the above tests, issue a cert and sleep well at night knowing its a job well done.
After all, its only a few extra sockets, whats so difficult??????