Evening all,

I found my first ever split concentric cable today. Running from an isolator up and into a flat. I was doing an EICR.

I could not verify where the cable is within the fabric of the building.

I failed the EICR on the grounds that the cable has no mechanical protection, no RCD protection or is even fused down.

I think the cable run is approximately 25 metres from the meter and isolator up into the flat.

Would anyone like to share there thoughts on this outcome?
 
EICRs don't fail they are satisfactory or unsatisfactory. The only major concern is no circuit protection.
 
How many flats / meters and how are the meters supplied, split from DNO cut out fuse or from a Ryfield distribution board or similar?
 
Now here lies your problem. If you introduce circuit protection you are obliged to give it additional protection.
Just hand the Report over and worry about solutions if they require them.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dumfries and Galloway
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Failed EICR on concentric feed to DB
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
Sonjohn84,
Last reply from
westward10,
Replies
7
Views
1,845

Advert

Back
Top