Evening all,

I found my first ever split concentric cable today. Running from an isolator up and into a flat. I was doing an EICR.

I could not verify where the cable is within the fabric of the building.

I failed the EICR on the grounds that the cable has no mechanical protection, no RCD protection or is even fused down.

I think the cable run is approximately 25 metres from the meter and isolator up into the flat.

Would anyone like to share there thoughts on this outcome?
 
Now here lies your problem. If you introduce circuit protection you are obliged to give it additional protection.
Just hand the Report over and worry about solutions if they require them.
 

Reply to Failed EICR on concentric feed to DB in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
I agree, it's not an immediate danger so can't be a C2. Bad design though, so improvement recommended.
Replies
4
Views
3K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
No mate, it was more out of curiosity than anything else. I see plenty in the high rise blocks that we fibre up that makes me cringe. See plenty...
Replies
3
Views
460
  • Question
I suspect you are not competent to be undertaking these works.
    • Optimistic
    • Funny
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top