I found my first ever split concentric cable today. Running from an isolator up and into a flat. I was doing an EICR.

I could not verify where the cable is within the fabric of the building.

I failed the EICR on the grounds that the cable has no mechanical protection, no RCD protection or is even fused down.

I think the cable run is approximately 25 metres from the meter and isolator up into the flat.

Would anyone like to share there thoughts on this outcome?
 
EICRs don't fail they are satisfactory or unsatisfactory. The only major concern is no circuit protection.
 
How many flats / meters and how are the meters supplied, split from DNO cut out fuse or from a Ryfield distribution board or similar?
 
Now here lies your problem. If you introduce circuit protection you are obliged to give it additional protection.
Just hand the Report over and worry about solutions if they require them.
 

Reply to Failed EICR on concentric feed to DB in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
623
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock