I have installed a fan from the lighting switch to bathroom do i need to use a spur for the fan or can i go direct
The extractor fan doesn't neccessarily need an isolator.
Please read:
Bathroom extractor fans and 3 pole isolation, a source of much controversy
We are discussing 314.4.
314.4 requires that where there is more than one final circuit, each final circuit must be supplied from a separate way at a distribution board.
If 'the cable coming off the load side of an FCU is it's own circuit', then what kind of a circuit is it?
If it is a final circuit, then it does not comply with BS7671, as it is not supplied from a separate way at a distribution board.
If it is a distribution circuit, then it must be supplying either a DB or switch gear.
Is it supplying a DB or switchgear, or is it some other kind of circuit which is not defined in BS7671?
When we test continuity of RFC conductors, we are required to record the highest measured value of R1+R2. The measurements are taken at each point on the RFC including any spurs, and the highest reading recorded.
We do not record the highest value measured on the RFC, and then list spurs as separate circuits and record their values separately.
As for your question, I would treat the whole circuit as one circuit, I would not attempt to separate the lighting circuit into two circuits, one for the lights and another for the bathroom light and fan.
As such I would list the lighting circuit protective device as the protective device.
You can do that ezzzekiel, but I would expect it to be noted as a departure on any certification, and I would further expect you to ensure that it provides the same degree of safety as would be achieved by compliance with the Regulations.
It may well be the third time that you've asked the question, I'm still struggling to see it's relevance.This is the third time I've asked this and you haven't even mentioned it.
WHY, if you can't have a circuit using a BS 1362 fuse, do they provide Zs values for them in the regs. I've never seen a distribution board with 3A and 13A plug-top fuses in them.
So what exactly is the circuit the FCU supplies, is it not a final circuit?We do not need to disregard Regulation 314.4 as the lighting final circuit itself complies with it as it's origin is the distribution board.
The FCU is supplied by the final circuit and itself supplies a circuit for the light and fan in the bathroom.
The reg you're referring to regarding RCD protection says that "Additional protection shall be provided for all circuits of the loacation...."
If what you're suggesting was true then surely it would say "Additional protection shall be provided for all final circuits supplying equipment in a location containing a bath or shower...." or something along those lines.
At the end of the day it's down to how each individual interprets the regulations.
So what exactly is the circuit the FCU supplies, is it not a final circuit?
Why would the wording be all final circuits? That would then allow distribution circuits to be unprotected.
In fact, it could be that the Regulation is not just for circuits that supply equipment in such locations, but also for circuits that pass through to supply equipment in other locations.
It may well be down to how an individual interprets the Regulations, although how you can interpret 314.4, and the very clear information provided in Appendix 15, in any other way than as it is written, is a mystery to me.
Of course, it may just be the case that you do not want to comply with 701.411.3.3 for whatever reason and are trying to make excuses?
Or:The reg is for all circuits of the location, not all circuits supplying the location.
I know Appendix 15 is not a Regulation, it is there to provide information in relation to the Regulations.If other circuits were passing through the location they would probably be concealed in walls or above ceilings so they would not strictly be in the location. If these circuits were installed before the requirement for RCDs then you have no obligation to bring them upto current standards as you haven't worked on these circuits.
JUD, this is becoming very tedious.
I suggest that if you can't put up then shut up.
I've answered your pointless question about Zs valus for BS1362 fuses, why won't you answer my question about what type of circuit is being supplied by the FCU?
Is it just because you know that the circuit must be a final circuit and as such is not accepted by BS7671 to be supplied from anything other than a distribution board?
A kettle meets the requirements of the definition of a circuit in Part 2, but I wouldn't call it a circuit.
I have no idea why you have stated:
Or:
I know Appendix 15 is not a Regulation, it is there to provide information in relation to the Regulations.
Should we then ignore the Tables for time/current characteristics of overcurrent protective devices in Appendix 3, the Tables for current carrying-capacities of cables in Appendix 4, the figures for voltage drop in Appendix 12, etc. as they also are not Regulations?
Or is it we just ignore the information that doesn't tally with your point of view?
JUD, this is becoming very tedious.
I suggest that if you can't put up then shut up.
I've answered your pointless question about Zs valus for BS1362 fuses, why won't you answer my question about what type of circuit is being supplied by the FCU?
Is it just because you know that the circuit must be a final circuit and as such is not accepted by BS7671 to be supplied from anything other than a distribution board?
A kettle meets the requirements of the definition of a circuit in Part 2, but I wouldn't call it a circuit.
I know Appendix 15 is not a Regulation, it is there to provide information in relation to the Regulations.
Should we then ignore the Tables for time/current characteristics of overcurrent protective devices in Appendix 3, the Tables for current carrying-capacities of cables in Appendix 4, the figures for voltage drop in Appendix 12, etc. as they also are not Regulations?
Or is it we just ignore the information that doesn't tally with your point of view?
JUD how will an RCD limit touch voltages if the fault is on a part of the circuit before the RCD?
The RCD will not detect the fault, and so will not operate.
JUD the fault current won't only take the path of least resistance, it will be distributed across all paths according to their resistance.A fault current on a part of the circuit before the RCD will take the path of least resistance i.e back to earth through the cpc and along the normal earth fault loop path and, if Zs for the circuit is within limits which it should be, take out the main breaker/fuse.
I was under the impression you'd both decided to agree to disagree!
Maybe the mods should step in!
:19:
If an existing circuit of a location containing a bath or shower is extended, at least the extended part of the existing circuit must be provided with RCD protection. Supplementary bonding in a bathroom or shower room must be provided unless all the requirements in the 17th Edition for the omission of supplementary bonding are met.
The IET do, and it is that the the circuit requires RCD protection.I thought the info in the link to the ESC website I provided would have made mine and others cases.
spin, I agree with Murdoch, let's just agree to disagree.
At the end of the day only the IET could give a definitive answer as to what is required.
The ESC or NICEIC do not write the Regulations.However back to the original op, the following extract taken from ESC and Niceic Guidlines
If an existing circuit of a location containing a bath or shower is extended, at least the extended part of the existing circuit must be provided with RCD protection. Supplementary bonding in a bathroom or shower room must be provided unless all the requirements in the 17th Edition for the omission of supplementary bonding are met