awkward one.. situ. is the room contains a sealed shower unit and toilet. shower cubicle is one of those fancy things, all enclosed with it's own fan in the top. my thoughts were to duct this the 4" up to the ceiling and out through the soffit and if the builtin fan was not powerful enough, to add an in line fan in the attic. the builder says that building regs. stipulate that the fan has to ventilate the toilet as well, so needs to be in the wall. is he right? because outside access is not possible due to fragile conservatiory roof. if it makes any difference, the room has an opening window. this could, at a push, give access to reach through and fit grille. your thoughts please, gentlemen.
 
If you have just a toilet with a opening window you don't need a fan at all, now because the shower has its own fan and your venting this out side I'd say it was fine.

we have the same sort of shower with a fan but ours just blows out into the room,
we do have another extractor fan though.
 
According to Part F, if the room has a window which opens to 30 degrees or more, the opening part of the window must be 1/20th of the room's floor area to remove the need for the fan. If it opens to less than 30 degrees then it needs to be 1/10th of the floor area.
 
According to Part F, if the room has a window which opens to 30 degrees or more, the opening part of the window must be 1/20th of the room's floor area to remove the need for the fan. If it opens to less than 30 degrees then it needs to be 1/10th of the floor area.

is that with regard to the shower or the toilet? at a guess the opening window is > 30deg. and about 5sq.ft. the floor area is 80sq.ft.
 
It's for bathrooms including shower rooms and those containing 'sanitary provision'. BTW, if it's a bathroom refurb it doesn't need to have a fan fitted unless there was one in already (Part 'F' 7.23).
 
it was a bedroom before. need to get it right as LABC will be coming to sign the job off.
 
Ah OK, in which case it's an extractor as per new build. The shower fan will be acceptable on it's own and you have the opening window size as mentioned. The other requirement is a 10mm gap under the door (7600 square mm).
 