C
Conteh
Done a condition report on a old mains board, everything good apart from ring final, got 0.55 nn 33.7ll and 3.8 on ee, changed board to main switch and rcbos, carried out a full accessory swap on all sockets and fuse spares in house, found some bad practice, twisted lives, n and earth's, no sleeving all things to add to the high resistance problem. Retested board end to end 0.55nn 0.90 ee open ll. So changed the 32 rcbo to 2x16a rcbos broke the ring in half having 5 sockets on one side and 6 on the other. Rcbo trips! Any idea what I'm doing wrong?
I know the information isn't details but fire away with questions.
Help ?
Bit confused with what tests you’ve done mate?...and are you saying you found a fault and then changed the board without finding the fault first??
Ignore me just read ya post properly...
Help ?
What type of wiring is employed?
yeah n/e fault possible ,you have swapped the 32 amp for 2 radials .yes. i hate it when some body's trying to wind up a elastic band on a pc or phone .lol.
what was the r1& r2 then .
Got to be summat wrong with the discrepancy with LL and NN readings, bad connection in the sockets, bad connection during testing, who knowns from afar? or the competence of the tester.
so L to L was 33 ohms, changed all the sockets and now it is open circuit end to end?
could it have been a poor connection somewhere giving a high resistance originally, now you have changed all sockets etc and its gone open circuit maybe a wire has come out of a terminal when you pushed sockets into boxes??
i would be checking the ring out with a wander lead.
edit, in the space of 4 minutes, 4 of us have basically had the same thoughts!!!
Assuming he/she comes back.
When you changed all the sockets did you check the ring as you were working your way around to prove it is a ring or remove all the old sockets and check and prove each leg to locate the fault if there is one?
Guys and girls I'm sorry for my poor attendance to class, having said that.
Just 1 rcbo trips, I connected L and N at 1 side of the circuit and simply tested continuity with the plug in lead, done the same test on the other side of the ring, I have found the break on the LL but repairing it isn't possible without damage to carpets or walls that the client isn't prepared to do, it could be a junction box. Yes. So I decided to split the ring into two radials, but 1 rcbo trips and can't understand why.
I did do I end to end on LL and got 33.7 ohms before the mains change, I then done a full accessory swap and now have open ring, I then checked all the sockets I swapped and there doesn't seem to be a break behind them.
I didn't check for a ring when installing the accessories, i will say that all the lives, N and E were twisted together before my works. The possibility of a break after the fact is high would you agree? I just don't know if to continue with finding the fault giving the clients limitations, or finding why 1 rcbo trips when splitting the ring.
Cheers